Re: PORTACRYO PRESSURE VESSEL - LIQUID ARGON

Rate this topic


Guest guest

Recommended Posts

Dear Sadiksaheb,

If it is not covered under SMPV rules,then

it may to get covered under The gas cylinder rules 2004.

Please refer the attachment for definition.

Regards.

M.Balachandran,

sadiksaheb.badiger@...

Sent by: indiansafetyprofessionals

19/12/06 06:36 PM

To

indiansafetyprofessionals ,

REC_HELPS

cc

Subject

PORTACRYO

PRESSURE VESSEL - LIQUID ARGON

Dear All

Can any body clarify on the following

issue if you are having already such

installation in your organisation.

1. We are planning to install PORTACRYO

pressure vessel to store Liquid Argon which

is having the capacity of 972

lits i.e less than 1000 lits.

2. Filling of the vessel to be done

from the road tanker and gas supplier

who is supplying the liquid Argon

is having the license for transporting

the liquid Argon.

3. As per SMPV rules this does not

attract the license for storage since

the vessel is less than 1000 lits capacity.

As per CCOE licence can not be

issued for the above vessel and also

we can not fill the liquid Argon

from tanker other than license premises.

Please share your views if any such

installations are done in your organisation,

how this is complied.

Best Regards

Badiger

_______________________________

Badiger SL

Manager- Environment,Health & Safety

Kennametal India limited

8/9 Mile, Tumkur Road

Bangalore-73

India

Phone : 22198118

Fax : 28394494

Cell : 9845512184

Please consider your environmental responsibility before printing this

e-mail

This e-mail message may contain privileged and/or confidential information,

and is intended to be received only by persons entitled to receive such

information. If you have received this e-mail in error, please notify the

sender immediately. Please delete it and all attachments from any servers,

hard drives or any other media. Other use of this e-mail by you is strictly

prohibited.

Disclaimer :

Information contained and transmitted by this E-MAIL is proprietary to

TotalFinaElf India Limited and is intended for use only by the individual

or entity to which it is addressed, and may contain information that is

privileged, confidential or exempt from disclosure under applicable law.

If this is a forwarded message, the content of this E-MAIL may not have

been sent with the authority of the Company. If you are not the intended

recipient, an agent of the intended recipient or a person responsible for

delivering the information to the named recipient, you are notified that

any use, distribution, transmission, printing, copying or dissemination

of this information in any way or in any manner is strictly prohibited.

If you have received this communication in error, please delete this mail

& notify us immediately at notes@...

Link to comment
Share on other sites

Dear Sadik Saheb,

1. It is not falling under SMPV because,for SMPV rule the license is applicable above 1000 L capacity.

2. Ready made 1 KL Vessels are supplied by many suppliers.

3. For details about the cry vessel please contact,also they guide about the statutory requirements.

ABS Towers, 4th floor, Old Padra Road, Vadodara 390 007, Gujarat, India

Tel: +91 265 2343125 (Main), 2335912,2343226

Fax +91 265-2333398,2341449

Email: vkalaria@... , mktg@... , Website: www.inoxindia.com

Thanks & regards

R. V.Patil

-----Original Message-----From: indiansafetyprofessionals [mailto:indiansafetyprofessionals ]On Behalf Of balachandran.m@...Sent: Tuesday, December 19, 2006 7:19 PMTo: sadiksaheb.badiger@...Cc: indiansafetyprofessionals ; REC_HELPS Subject: Re: PORTACRYO PRESSURE VESSEL - LIQUID ARGONDear Sadiksaheb, If it is not covered under SMPV rules,then it may to get covered under The gas cylinder rules 2004. Please refer the attachment for definition. Regards. M.Balachandran,

sadiksaheb.badiger@... Sent by: indiansafetyprofessionals 19/12/06 06:36 PM

To

indiansafetyprofessionals , REC_HELPS

cc

Subject

PORTACRYO PRESSURE VESSEL - LIQUID ARGON

Dear All Can any body clarify on the following issue if you are having already such installation in your organisation. 1. We are planning to install PORTACRYO pressure vessel to store Liquid Argon which is having the capacity of 972 lits i.e less than 1000 lits. 2. Filling of the vessel to be done from the road tanker and gas supplier who is supplying the liquid Argon is having the license for transporting the liquid Argon. 3. As per SMPV rules this does not attract the license for storage since the vessel is less than 1000 lits capacity. As per CCOE licence can not be issued for the above vessel and also we can not fill the liquid Argon from tanker other than license premises. Please share your views if any such installations are done in your organisation, how this is complied. Best RegardsBadiger _______________________________Badiger SLManager- Environment,Health & SafetyKennametal India limited8/9 Mile, Tumkur RoadBangalore-73IndiaPhone : 22198118Fax : 28394494Cell : 9845512184Please consider your environmental responsibility before printing this e-mail This e-mail message may contain privileged and/or confidential information, and is intended to be received only by persons entitled to receive such information. If you have received this e-mail in error, please notify the sender immediately. Please delete it and all attachments from any servers, hard drives or any other media. Other use of this e-mail by you is strictly prohibited.

Disclaimer : Information contained and transmitted by this E-MAIL is proprietary to TotalFinaElf India Limited and is intended for use only by the individual or entity to which it is addressed, and may contain information that is privileged, confidential or exempt from disclosure under applicable law. If this is a forwarded message, the content of this E-MAIL may not have been sent with the authority of the Company. If you are not the intended recipient, an agent of the intended recipient or a person responsible for delivering the information to the named recipient, you are notified that any use, distribution, transmission, printing, copying or dissemination of this information in any way or in any manner is strictly prohibited. If you have received this communication in error, please delete this mail & notify us immediately at notes@...

----------------------------------------------------------------------

The information contained in this electronic message and any

attachments to this message are intended for the exclusive use of the

addressee(s) and may contain confidential or privileged information. If

you are not the intended recipient, please notify the sender at Unichem

Laboratories Limited or it@... immediately and destroy all

copies of this message and any attachments.

----------------------------------------------------------------------

Link to comment
Share on other sites

Dear Balachandran,

Thanks for your response,

Issue is like

Explosive Department will

not issue licence under SMPV

rules since it is less than

1000 lits. but they will not allow

to do filling if it is not a

licence premises.

If you consider this as

Gas cylinder - As per Rule No

52 - No licence needed for filling

and possession in certain cases , we

need not obtain the licence since

it is one gas cylinder.

But we have to

fill this PORTOCRYO vessel in the

factory premises from the road tanker

which is licensed under SMPV rules. In

this situation how to fulfill the regulatory

requirement.

If any body is

having such installation please let me

know how they have considered to fulfill the

requirement.

Best Regards

Badiger

_______________________________

Badiger SL

Manager- Environment,Health & Safety

Kennametal India limited

8/9 Mile, Tumkur Road

Bangalore-73

India

Phone : 22198118

Fax : 28394494

Cell : 9845512184

Please consider your environmental responsibility before printing this

e-mail

This e-mail message may contain privileged and/or confidential information,

and is intended to be received only by persons entitled to receive such

information. If you have received this e-mail in error, please notify the

sender immediately. Please delete it and all attachments from any servers,

hard drives or any other media. Other use of this e-mail by you is strictly

prohibited.

balachandran.m@...

Sent by: indiansafetyprofessionals

12/19/2006 07:19 PM

To

sadiksaheb.badiger@...

cc

indiansafetyprofessionals ,

REC_HELPS

Subject

Re: PORTACRYO

PRESSURE VESSEL - LIQUID ARGON

Dear Sadiksaheb,

If it is not covered under SMPV rules,then it may to get covered under

The gas cylinder rules 2004.

Please refer the attachment for definition.

Regards.

M.Balachandran,

sadiksaheb.badiger@...

Sent by: indiansafetyprofessionals

19/12/06 06:36 PM

To

indiansafetyprofessionals ,

REC_HELPS

cc

Subject

PORTACRYO

PRESSURE VESSEL - LIQUID ARGON

Dear All

Can any body clarify on the following

issue if you are having already such

installation in your organisation.

1. We are planning to install PORTACRYO

pressure vessel to store Liquid Argon which

is having the capacity of 972

lits i.e less than 1000 lits.

2. Filling of the vessel to be done

from the road tanker and gas supplier

who is supplying the liquid Argon

is having the license for transporting

the liquid Argon.

3. As per SMPV rules this does not

attract the license for storage since

the vessel is less than 1000 lits capacity.

As per CCOE licence can not be

issued for the above vessel and also

we can not fill the liquid Argon

from tanker other than license premises.

Please share your views if any such

installations are done in your organisation,

how this is complied.

Best Regards

Badiger

_______________________________

Badiger SL

Manager- Environment,Health & Safety

Kennametal India limited

8/9 Mile, Tumkur Road

Bangalore-73

India

Phone : 22198118

Fax : 28394494

Cell : 9845512184

Please consider your environmental responsibility before printing this

e-mail

This e-mail message may contain privileged and/or confidential information,

and is intended to be received only by persons entitled to receive such

information. If you have received this e-mail in error, please notify the

sender immediately. Please delete it and all attachments from any servers,

hard drives or any other media. Other use of this e-mail by you is strictly

prohibited.

Disclaimer :

Information contained and transmitted by this E-MAIL is proprietary to

TotalFinaElf India Limited and is intended for use only by the individual

or entity to which it is addressed, and may contain information that is

privileged, confidential or exempt from disclosure under applicable law.

If this is a forwarded message, the content of this E-MAIL may not have

been sent with the authority of the Company. If you are not the intended

recipient, an agent of the intended recipient or a person responsible for

delivering the information to the named recipient, you are notified that

any use, distribution, transmission, printing, copying or dissemination

of this information in any way or in any manner is strictly prohibited.

If you have received this communication in error, please delete this mail

& notify us immediately at notes@...

Link to comment
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...