Re: Remedy attic air quality issues

Rate this topic


Guest guest

Recommended Posts

Don,

Are you sure that the attic exhaust fan is causing attic air containing formaldehyde (etc.) to enter the living area, or is it creating negative pressure in the living area that is pulling formaldehyde-contaminated air in from wall cavities or elsewhere? If so, provide a path of least resistance to the outdoors. That is, make sure the make-up air for the air being pulled into the attic from the living space is of good quality.

You may have more attic exhaust than you need. Especially in the heating season, you only need to make sure the house isn't negative relative to the attic. You don't need to move large volumes of air. Assuming you aren't exhausting air deliberately from the living space or from underneath it (basement or crawl), additional sources of negative pressure in the house would be from the return ductwork in a forced air system, or the venturi effect from cross-ventilation with windows open.

Sealing of all ceiling plane communication between the attic and living space can be difficult. You can use inexpensive smoke testing (Wizard Stick from www.zerotoys.com) to figure out some of the air leakage and air current pathways.

You need to ventilate the house, meaning indoor/outdoor air exchange in the living areas. Keep windows open or consider retrofitting a whole-house ventilation (ERV) system.

I will assume that when you refer to the mold under the sink being problematic, that you are reacting to low levels of MVOCs.

Sorry, I don't know anyone I can recommend in your area who specializes in working with people with chemical sensitivities, but you can search the IAQA website (www.iaqa.org) for local consultants and interview them. They shouldn't need to test if you can tell them where the problem areas are.

Consider that this is your first heating season in the house. Formaldehyde or other chemical offgassing may be occurring at a higher rate due to the heating system being in operation which warms building materials as well as the air.

Thanks for your post. Many of my clients have similar chemical hypersensitivity issues (often to MVOCs at very low concentrations), however there are a lot of professionals in the IAQ and medical fields who don't have any appreciation for the types of health effects you describe.

Steve Temes

AirWays Environmental Svcs.

Red Bank, NJ

In a message dated 11/10/2011 8:48:19 PM Eastern Standard Time, no_reply writes:

I just recently purchased (in August) a home in Mount Vernon WA. I have chemical intolerances. I believed the only issues I would have to remedy were the mold from leak under the kitchen sink and the new carpet. I have Reactive Airway Disorder and certain chemicals trigger bronchitis and other inflammatory reactions. I was surprised when the removal of the carpet did not end the bronchitis. It was when I went into the attic I realized that I was reacting to the formaldehyde in the OSB in the sub roof. A contractor friend recommended putting a gable fan to remove gases. The gable fan seemed to create a pressure that made the gases enter the interior even more strongly. I hired different handy men to seal the exposed OSB (between the wood lathes to which the original cedar shakes had been nailed. There is a gap between the lumber lathes). I had two coats of AFM Safe Seal and a coat of a no VOC primer applied. The formaldehyde continues to be a problem.

It is now cold here and the fan only comes on when it is about 60 degrees. I am not sure how to remedy this issue now. I need to find someone in my area who can give a consultation. BTW, the house has no eve vents or roof vents. The venting is solely through the two gable vents. This is a Japanese-like style roof with too levels. The lower level has zero venting. So when the heat creates formaldehyde gas off there really is no place upward for the gas to go (since the roof itself acts as a vapor barrier). This is a great architecturally designed home. I believe when they put the new roof on (before resale), they did not want to harm the aesthetics of the roof design. I have been told that it is now code to have roof and eve vents.

Does anyone active on this list live in northwest Washington State (Bellingham, Seattle, Mount Vernon)? I want to create a thoughtful remedy for this problem. I am looking for someone who may have IAQ expertise. I can find someone to do the work. BTW, the insulation in the attic is pathetic (some rock wool and two inch paper batted fiberglass) I need to do some research for tolerable insulation ( Mansville and Skytech have been recommended as options).

Thanks for any information, leads, or help you may render.

Don Paladin WSMCSN Owner

Sunergos2001@...

http://wsmcsn.s5.com

p.s. I have been an inactive member of this list for years.

Link to comment
Share on other sites

Don: OSB is advertised as having very low formaldehyde emissions. http://osbguide.tecotested.com/faq10 If you have formaldehyde emissions from your OSB, perhaps it was made in a non-standard manufacturing facility. As for the gable fan, does it exhaust gases from the attic or does it blow fresh air in? Your description implies that outside air is being blown in through one gable vent and exhausted through the other gable vent. It seems to me that it if both gable vents are the same size there should be insignificant positive pressure to cause polluted air to be blown through the ceiling into your living space. I don’t understand how a two-level roof with one attic could create a problem. Are the two attics unconnected to each other? Norm Gauss From: iequality [mailto:iequality ] On Behalf Of sunergos2001Sent: Thursday, November 10, 2011 4:52 PMTo: iequality Subject: Remedy attic air quality issues I just recently purchased (in August) a home in Mount Vernon WA. I have chemical intolerances. I believed the only issues I would have to remedy were the mold from leak under the kitchen sink and the new carpet. I have Reactive Airway Disorder and certain chemicals trigger bronchitis and other inflammatory reactions. I was surprised when the removal of the carpet did not end the bronchitis. It was when I went into the attic I realized that I was reacting to the formaldehyde in the OSB in the sub roof. A contractor friend recommended putting a gable fan to remove gases. The gable fan seemed to create a pressure that made the gases enter the interior even more strongly. I hired different handy men to seal the exposed OSB (between the wood lathes to which the original cedar shakes had been nailed. There is a gap between the lumber lathes). I had two coats of AFM Safe Seal and a coat of a no VOC primer applied. The formaldehyde continues to be a problem.It is now cold here and the fan only comes on when it is about 60 degrees. I am not sure how to remedy this issue now. I need to find someone in my area who can give a consultation. BTW, the house has no eve vents or roof vents. The venting is solely through the two gable vents. This is a Japanese-like style roof with too levels. The lower level has zero venting. So when the heat creates formaldehyde gas off there really is no place upward for the gas to go (since the roof itself acts as a vapor barrier). This is a great architecturally designed home. I believe when they put the new roof on (before resale), they did not want to harm the aesthetics of the roof design. I have been told that it is now code to have roof and eve vents. Does anyone active on this list live in northwest Washington State (Bellingham, Seattle, Mount Vernon)? I want to create a thoughtful remedy for this problem. I am looking for someone who may have IAQ expertise. I can find someone to do the work. BTW, the insulation in the attic is pathetic (some rock wool and two inch paper batted fiberglass) I need to do some research for tolerable insulation ( Mansville and Skytech have been recommended as options). Thanks for any information, leads, or help you may render.Don Paladin WSMCSN OwnerSunergos2001@...http://wsmcsn.s5.comp.s. I have been an inactive member of this list for years.

Link to comment
Share on other sites

Hi Norm,

Thank you for your reply. First, I do not know where the roofing contractor

obtained the osb sheeting for this roof. Please understand that I am

" hypersensitive " to formaldehyde. I am in the ONE PERCENT (not the billionaire

one percent) that is hypersensitive to formaldehyde. This was a result of buying

a mobile home in 1976 laden with the stuff. From that long term exposure I

developed Reactive Airway Disorder (bronchial and mucus lining inflammation).

Those standards you linked to do not say there is zero formaldehyde in the OSB.

(Please note Monsanto says that Roundup is non-toxic and not harmful ... but it

is very toxic for me). My pathways for detoxifying biocides (borates,

pesticides, formaldehydes, etc.) have been severely damaged.

The house is a custom built and architecturally designed home built in 1960. I

know the source of the environmental trigger is in the attic because my level of

reaction went up very high the two or three times I have tried to enter it.

There has been no new insulation added since 1960 (walls or attic). There has

been no painting done recently (within at least a year). I had the new carpet

removed from the slab floor. The slab is well drained with gutter being drained

to the storm sewer. The only mold I detect is from a leak under the sink in the

kitchen.The leak has been repaired. I will need to seal the cabinet that emits

mold odor.

Through deductive reasoning, that left the source being the OSB. Please

understand that my tolerance level of formaldehyde is pretty near zero.

The roof is like a Japanese style roof. There is a higher (like a pop up in the

center) roof with a higher pitch. The lower level roof has a lower pitch. The

only venting is being done in the the higher pitched roof. There are NO eves or

roof vents. There is only ONE attic connected with this bi-level roof. When the

lower roof has gases, there really is not easy venting access except through air

circulation through central pop-up roof where the vents are. It may be hard to

visualize because this is a custom designed roof.

I had an electrician put a gable fan on the east facing gable (the highest point

in the pop-up roof). The west gable vent remains open to air flow. I am assuming

he attached the fan so that it would blow air out of the attic. This would cause

it to suck air from the other vent and cracks in the house. My goal was to

create a pressure so that air flow would be able to access gases in the lower

roof. The design of the roof may not have been amendable to such a plan.

If you think of the lower pitched roof as being an envelop open to the larger

roof, that might help explain the air flow problem. There are ZERO vents in the

lower roof pitch. The house is not a square box. The bedroom is like a rectangle

attached to a larger rectangle. Maybe this is only confusing.

As you can see, it is not an easy venting issue. My brother in law who was a

contractor (now retired) recommended putting in roof vents in the lower roof.

The only issue I have with that is that will the roof vents change the IAQ so

that ALL attic air is being vented upward and outward. That is why the question

about IAQ and the attic. I want to be prudent in resolving this issue.

Again, thank you for your response.

Don Paladin WSMCSN

http://wsmcsn.s5.com

>

> Don:

>

>

>

> OSB is advertised as having very low formaldehyde emissions.

>

>

>

> http://osbguide.tecotested.com/faq10

>

>

>

> If you have formaldehyde emissions from your OSB, perhaps it was made in a

> non-standard manufacturing facility.

>

>

>

> As for the gable fan, does it exhaust gases from the attic or does it blow

> fresh air in? Your description implies that outside air is being blown in

> through one gable vent and exhausted through the other gable vent. It seems

> to me that it if both gable vents are the same size there should be

> insignificant positive pressure to cause polluted air to be blown through

> the ceiling into your living space.

>

>

>

> I don't understand how a two-level roof with one attic could create a

> problem. Are the two attics unconnected to each other?

>

>

>

> Norm Gauss

>

>

>

>

>

> From: iequality [mailto:iequality ] On Behalf

> Of sunergos2001

> Sent: Thursday, November 10, 2011 4:52 PM

> To: iequality

> Subject: Remedy attic air quality issues

>

>

>

>

>

> I just recently purchased (in August) a home in Mount Vernon WA. I have

> chemical intolerances. I believed the only issues I would have to remedy

> were the mold from leak under the kitchen sink and the new carpet. I have

> Reactive Airway Disorder and certain chemicals trigger bronchitis and other

> inflammatory reactions. I was surprised when the removal of the carpet did

> not end the bronchitis. It was when I went into the attic I realized that I

> was reacting to the formaldehyde in the OSB in the sub roof. A contractor

> friend recommended putting a gable fan to remove gases. The gable fan seemed

> to create a pressure that made the gases enter the interior even more

> strongly. I hired different handy men to seal the exposed OSB (between the

> wood lathes to which the original cedar shakes had been nailed. There is a

> gap between the lumber lathes). I had two coats of AFM Safe Seal and a coat

> of a no VOC primer applied. The formaldehyde continues to be a problem.

>

> It is now cold here and the fan only comes on when it is about 60 degrees. I

> am not sure how to remedy this issue now. I need to find someone in my area

> who can give a consultation. BTW, the house has no eve vents or roof vents.

> The venting is solely through the two gable vents. This is a Japanese-like

> style roof with too levels. The lower level has zero venting. So when the

> heat creates formaldehyde gas off there really is no place upward for the

> gas to go (since the roof itself acts as a vapor barrier). This is a great

> architecturally designed home. I believe when they put the new roof on

> (before resale), they did not want to harm the aesthetics of the roof

> design. I have been told that it is now code to have roof and eve vents.

>

> Does anyone active on this list live in northwest Washington State

> (Bellingham, Seattle, Mount Vernon)? I want to create a thoughtful remedy

> for this problem. I am looking for someone who may have IAQ expertise. I can

> find someone to do the work. BTW, the insulation in the attic is pathetic

> (some rock wool and two inch paper batted fiberglass) I need to do some

> research for tolerable insulation ( Mansville and Skytech have been

> recommended as options).

>

> Thanks for any information, leads, or help you may render.

> Don Paladin WSMCSN Owner

> Sunergos2001@... <mailto:Sunergos2001%40yahoo.com>

> http://wsmcsn.s5.com

>

> p.s. I have been an inactive member of this list for years.

>

Link to comment
Share on other sites

Steve, Wouldn't you always be creating a negative pressure effect in a house by

opening windows?

>

>

> You may have more attic exhaust than you need. Especially in the heating

> season, you only need to make sure the house isn't negative relative to the

> attic. You don't need to move large volumes of air. Assuming you aren't

> exhausting air deliberately from the living space or from underneath it

> (basement or crawl), additional sources of negative pressure in the house

would be

> from the return ductwork in a forced air system, or the venturi effect from

> cross-ventilation with windows open.

>

Link to comment
Share on other sites

I'm not an indoor air quality professional but had an air leaky attic. It's

possible if there is a lot of air leakage between house and attic that fan is

creating a lot of air movement in house, perhaps sucking it out of attic but

perhaps make up air is coming from down in house. In order for that air to

leave house out attic, it needs makeup air which it could be pulling down from

attic also or from some other unclean area of house, wall cavities, etc. I had

a lot of air leakage betw attic and house that caused problems with too much air

movement betw unclean areas, basement, attic and interior walls. Fan may have

just increased the movement of gasses all through house.

>

> I just recently purchased (in August) a home in Mount Vernon WA. I have

chemical intolerances. I believed the only issues I would have to remedy were

the mold from leak under the kitchen sink and the new carpet. I have Reactive

Airway Disorder and certain chemicals trigger bronchitis and other inflammatory

reactions. I was surprised when the removal of the carpet did not end the

bronchitis. It was when I went into the attic I realized that I was reacting to

the formaldehyde in the OSB in the sub roof. A contractor friend recommended

putting a gable fan to remove gases. The gable fan seemed to create a pressure

that made the gases enter t

Link to comment
Share on other sites

P.S. to my post. I notice you say fan put in highest part of roof. Research

says that formaldehyde is heavier than air so settles to low areas so perhaps if

fan is in highest are, it is not venting out the formaldehyde. I had

professional air sealing done in my attic to solve air leakage problems betw

attic and house.

http://epa.gov/Region7/education_resources/teachers/ehsstudyehs10.htm

http://epa.gov/Region7/education_resources/teachers/ehsstudy/ehs10.htm

>>

> Hi Norm,

> Thank you for your reply. F

Link to comment
Share on other sites

Jim, I was suggesting a possibility that I hoped professionals here would

comment on. I know I'm not an expert but as far as references go, this is from

the epa saying formaldehyde would seek low places. This may be over time and in

still air as you suggest but it wasn't from a poor reference.

>

> Barb

> Gases tend to mix quite well in large spaces and it is very unlikely that the

formaldehyde 'settles' because it is heavier than air (even if it was from the

underside of the sloped roof). Removing air from the attic removes formaldehyde

that is mixed in with the air. For seconds to minutes after a gas is locally

introduced it will not be in equilibrium, but after hours the mixing is usually

very good indeed. A little science can mislead badly. Check the background of

your sources carefully.

>

> Jim H. White SSC

>

> Re: Remedy attic air quality issues

>

> I notice you say fan put in highest part of roof. Research says that

formaldehyde is heavier than air so settles to low areas so perhaps if fan is in

highest are, it is not venting out the formaldehyde. I had professional air

sealing done in my attic to solve air leakage problems betw attic and house.

>

>

> http://epa.gov/Region7/education_resources/teachers/ehsstudy/ehs10.htm

Link to comment
Share on other sites

Yes, I can see a tremendous number of variables. Complicated.

>

> Barb

> As Steve says there are several ways that air is sucked out by open windows,

depending on their orientation to the wind. If wind comes directly at a wall,

that wall and the openings in it will be pressurized compared to the average

outside pressure (except near the corners). All of the other surfaces will be

depressurized; the most

Link to comment
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...