Bob,

In my opinion, you've made very good and valid points as they relate to evaluation of "good" or "acceptable" IAQ, particularly "fan on and fan off", wind effects, and if seeking to identify specific gasses due to expressed health concerns, measuring and evaluating real chemical concentrations certainly makes sense.

Leaving the attempts to define "good IAQ" and investigation of specific health complaints out of the discussion for a moment, don't you agree that using CO2 provides a simple, cost-effective and reasonable estimation of air exchange rates in order to simply answer the question "is the outdoor air intake (ventilation rate) provided within generally accepted parameters?", as a starting point?

"Cost-effective" being a key component of my reasoning, as many clients view expenditures for our services as being about as pleasant as a root canal.

Of course, specific health complaints, differences in interior HVAC system distribution settings, activities performed and even relative location of different areas within the structure, ambient conditions, etc., etc. will all impact whether or not the IAQ is "acceptable" for the occupants in specific areas, and may indicate the need for subsequent more detailed studies.

Chuck Reaney, CIEC, CIAQP

Using CO2

Using CO2 to measure air exchanges is not an accurate and a misleading evaluation. 1. CO2 concentrations will decrease simply due to diffusion through the building walls. (Yes, it does go through walls unless they are steel lined). 2. You can only use CO2 if you test the building on various days with different wind speeds. The difference in the CO2 decay due to wind speeds will give an indication of infiltration air changes.3. You need to account for the driving force(s) for the decrease in concentration. What is the room ventilation rate? Was the fan on? What was the external wind speed? What was the exterior wall pressure differential? etc?4. What is the difference in decay rates with the fan on and off?5. Claiming that CO2 is a measure of air changes to eliminate body odor is an illusion. Odor perception by women varies by the time of month and pregnancy. Further, sensitive people odor detection can be very low. 6. Claiming that CO2 based air change rate is indicative of acceptable IAQ is baseless. e.g. What about basements with soil gas emissions? What about levels of other chemicals in the environment?I have done numerous CO2 studies, tracer gas studies and trace chemical analysis. The only reliable indicator of acceptable IAQ is to measure the real chemical concentrations. As us older people remember, this CO2 argument was used to justify 62-1981-which was an "unhealthful" ventilation standard in ASHRAEs own words. Let's not make this same mistake again. Dr. Bob

Posted

Chuck:I would agree strongly that using measurements of CO2 is a basic very powerful tool for assessing actual ventilation performance in buildings. Each measurement reflects the dynamic interaction of the variables includes the amount of outdoor air delivery, the number of people present, their activity levels,and their duration of occupancies. Focusing on the maximum and minimum values for each locationcan yield a lot of information on HVAC operational performance including the completeness of the overnight flushout and an estimate of the least amount of ventilation provided.One of the challenges, however, is the accuracy of the CO2 used. Much better accuracy can be obtainedby using one of the centralized, shared-sensor monitoring approaches if there are enough locationsto be monitored to justify the expense of installing the sampling lines.Another advantage provided by the shared-sensor approach is that dew point can be easily measured simultaneously with each CO2 reading, and so their is now diagnostic feedback on moisture managementperformance as well as ventilation performance. Life Energy Associateswww.LifeEnergyAssoc.com20 Darton StreetConcord, MA 01742 Using CO2

Using CO2 to measure air exchanges is not an accurate and a misleading evaluation. 1. CO2 concentrations will decrease simply due to diffusion through the building walls. (Yes, it does go through walls unless they are steel lined). 2. You can only use CO2 if you test the building on various days with different wind speeds. The difference in the CO2 decay due to wind speeds will give an indication of infiltration air changes.3. You need to account for the driving force(s) for the decrease in concentration. What is the room ventilation rate? Was the fan on? What was the external wind speed? What was the exterior wall pressure differential? etc?4. What is the difference in decay rates with the fan on and off?5. Claiming that CO2 is a measure of air changes to eliminate body odor is an illusion. Odor perception by women varies by the time of month and pregnancy. Further, sensitive people odor detection can be very low. 6. Claiming that CO2 based air change rate is indicative of acceptable IAQ is baseless. e.g. What about basements with soil gas emissions? What about levels of other chemicals in the environment?I have done numerous CO2 studies, tracer gas studies and trace chemical analysis. The only reliable indicator of acceptable IAQ is to measure the real chemical concentrations. As us older people remember, this CO2 argument was used to justify 62-1981-which was an "unhealthful" ventilation standard in ASHRAEs own words. Let's not make this same mistake again. Dr. Bob

Posted

don't you agree that using CO2 provides a simple, cost-effective and reasonable estimation of air exchange rates in order to simply answer the question "is the outdoor air intake (ventilation rate) provided within generally accepted parameters?", as a starting point?Chuck, I have seen way too many IAQ cases whether the CO2 level was fine, but chemical and other biological materials levels were not. As NIOSH showed in their numerous IAQ investigations- more outside air - reduces the impact and incidence of IAQ complaints. In my experience, implying to a client the amount of outside air is "acceptable" based on CO2 levels does not deal with the need for more outside air to deal with other problems. Further, the issues of adequate air mixing within specific spaces, and ventilation velocity also have an impact on IAQ complaints. There are specific IAQ standards that deal with ventilation velocity. Lastly, I recently raised the question (in an IH legal ethic presentation by a lawyer) of whether it is unethical for an IH or anyone to ignore IAQ standard in other countries?He said that it "behooves" IHs to use this information when no US standards exists. Look up the definition of "behooves". It was an excellent warning to the IHs in the room. Did they listen?Bob

Posted



and Bob,

I agree with the statements made by both of you. My main point was that I believe it is most economical to use CO2 to evaluate ONLY HVAC/ventilation performance, as indicated, and I agree strongly that excessive ventilation rates would be necessary in order to deal with other very real issues involving the presence of various contaminants.

Perhaps rather than stating using CO2 in evaluating air exchange rates as an isolated parameter "as a starting point", I would have been more accurate to say "as one of the evaluations" or even the last evaluation to be performed, IF we're looking for "problems" within a building.

In fact, a better starting point, in investigating potential indoor contaminant issues MAY be to reduce the ventilation rate temporarily so that the presence of contaminants would in fact be greater (less diluted) for a brief duration, making them more easily measurable and identifiable. Once they are identified and the sources mitigated, evaluation of the HVAC performance and associated ventilation rates, and moisture control would certainly make a lot of sense.

As usual, these "theoretical" discussions leave out many significant variables and considerations, and every structure presents its own set of circumstances and challenges, so it's difficult if not impossible, to draw any "one size fits all" conclusions.

As an example of the lack of understanding by clients and the challenges that are often involved, I was asked about a year ago, to investigate what might be causing headaches, fatigue, respiratory and eye irritation in a SINGLE OFFICE SUITE, with highly variable occupancy rates, located on the sixth floor in a 12 story structure on the shores of a major river. The best part of this challenge was that I was not allowed access to any other areas of the building, including the roof, & HVAC systems, and no records regarding pesticide use, maintenance schedules, cleaning chemicals, tenant list, occupant activities beyond this one office suite, etc. were available for review.

Needless to say, after I presented the proposal, which necessitated an expensive "shotgun" approach, the client decided it was better to live with the long-term discomfort than the short-term pain of having to pay for numerous studies, many of which would not have been necessary, if I would have been able to have full access to the structure, systems and records in order to develop a targeted approach.

Even if it was an unrestricted investigation, the costs would have been fairly significant, and since the tenant, not the Owner or Management company was footing the bill, it's likely that they still would have decided to do nothing based upon financial considerations, and that's my major point in this discussion. It seems to me that many clients think that there's a "magic meter" that we can use to stand in the middle of an area, turn it on, spin around three times, and it will reveal ALL of the "nasties" and associated issues in a structure. So while most of what you are both saying is absolutely accurate and valid in a perfect world, with only a few possible minor differences in approach that we may not be 100% in agreement on, the money is usually an undeniable and substantial constraint in the real world, forcing us to use a large degree of common sense and anecdotal information, as the more "scientific" approach in collecting even marginally statistically significant data, is too often financially unattractive to clients.

I realize that we're getting a bit off topic with all of this, but this is where the ideal meets the real world, at least in my world.

Thank you for your feedback.

Additional thoughts?

Chuck

Using CO2

Using CO2 to measure air exchanges is not an accurate and a misleading evaluation. 1. CO2 concentrations will decrease simply due to diffusion through the building walls. (Yes, it does go through walls unless they are steel lined). 2. You can only use CO2 if you test the building on various days with different wind speeds. The difference in the CO2 decay due to wind speeds will give an indication of infiltration air changes.3. You need to account for the driving force(s) for the decrease in concentration. What is the room ventilation rate? Was the fan on? What was the external wind speed? What was the exterior wall pressure differential? etc?4. What is the difference in decay rates with the fan on and off?5. Claiming that CO2 is a measure of air changes to eliminate body odor is an illusion. Odor perception by women varies by the time of month and pregnancy. Further, sensitive people odor detection can be very low. 6. Claiming that CO2 based air change rate is indicative of acceptable IAQ is baseless. e.g. What about basements with soil gas emissions? What about levels of other chemicals in the environment?I have done numerous CO2 studies, tracer gas studies and trace chemical analysis. The only reliable indicator of acceptable IAQ is to measure the real chemical concentrations. As us older people remember, this CO2 argument was used to justify 62-1981-which was an "unhealthful" ventilation standard in ASHRAEs own words. Let's not make this same mistake again. Dr. Bob

Posted

Chuck:Your anecdote reminds me of the client I had that initially did not want to have me talk to the occupants of a space as part of my evaluation.I had to convince him that this was part of the assessment.My first step in dealing with a problem building is to LISTEN to the occupants with the concerns and then formulate a hypothesis to explain these reported symptoms. Sometimes this suggests determining the ventilation rate, sometimes it doesn't.In a more poractive evaluation, determining the actual ventilation rate is a necessary part of the evaluation.As we move forward, andmore people realize how much HVAC operation can vary from original intent, I'm seeing a movment toward "smart building" where the operators have continuous diagnostic feedback on both ventilation and moisture management performance to document that a healthy and productive environment continues to be provided in terms of these parameters. Life Energy Associateswww.LifeEnergyAssoc.com20 Darton StreetConcord, MA 01742 Using CO2

Using CO2 to measure air exchanges is not an accurate and a misleading evaluation. 1. CO2 concentrations will decrease simply due to diffusion through the building walls. (Yes, it does go through walls unless they are steel lined). 2. You can only use CO2 if you test the building on various days with different wind speeds. The difference in the CO2 decay due to wind speeds will give an indication of infiltration air changes.3. You need to account for the driving force(s) for the decrease in concentration. What is the room ventilation rate? Was the fan on? What was the external wind speed? What was the exterior wall pressure differential? etc?4. What is the difference in decay rates with the fan on and off?5. Claiming that CO2 is a measure of air changes to eliminate body odor is an illusion. Odor perception by women varies by the time of month and pregnancy. Further, sensitive people odor detection can be very low. 6. Claiming that CO2 based air change rate is indicative of acceptable IAQ is baseless. e.g. What about basements with soil gas emissions? What about levels of other chemicals in the environment?I have done numerous CO2 studies, tracer gas studies and trace chemical analysis. The only reliable indicator of acceptable IAQ is to measure the real chemical concentrations. As us older people remember, this CO2 argument was used to justify 62-1981-which was an "unhealthful" ventilation standard in ASHRAEs own words. Let's not make this same mistake again. Dr. Bob

Posted

Chuck:Yes, educating the client can often be difficult,but I consider myself lucky to have a profession that lets mehelp people and periodically be mentally challenging as I put the clues together to form a hypothsis.It's not perfect, but it is still very good.Life Energy Associateswww.LifeEnergyAssoc.com20 Darton StreetConcord, MA 01742 Using CO2

Using CO2 to measure air exchanges is not an accurate and a misleading evaluation. 1. CO2 concentrations will decrease simply due to diffusion through the building walls. (Yes, it does go through walls unless they are steel lined). 2. You can only use CO2 if you test the building on various days with different wind speeds. The difference in the CO2 decay due to wind speeds will give an indication of infiltration air changes.3. You need to account for the driving force(s) for the decrease in concentration. What is the room ventilation rate? Was the fan on? What was the external wind speed? What was the exterior wall pressure differential? etc?4. What is the difference in decay rates with the fan on and off?5. Claiming that CO2 is a measure of air changes to eliminate body odor is an illusion. Odor perception by women varies by the time of month and pregnancy. Further, sensitive people odor detection can be very low. 6. Claiming that CO2 based air change rate is indicative of acceptable IAQ is baseless. e.g. What about basements with soil gas emissions? What about levels of other chemicals in the environment?I have done numerous CO2 studies, tracer gas studies and trace chemical analysis. The only reliable indicator of acceptable IAQ is to measure the real chemical concentrations. As us older people remember, this CO2 argument was used to justify 62-1981-which was an "unhealthful" ventilation standard in ASHRAEs own words. Let's not make this same mistake again. Dr. Bob

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...