Guest guest Posted December 31, 2009 Report Posted December 31, 2009 Dave, This certainly is not a new problem. Back in 1990, I investigated a major indoor air quality problem in the Dupage County Judicial Office Building. 400 people went to the hospital, a $12,000,000 litigation suite, and $4,000, 000 to fix the building. The VAV boxes in the court rooms would sense temperature and not the number of people. This was especially, a problem during the AC season, the court rooms would reach set point with hundreds of people in them and no ventilation. This was made significantly worse, by pre cooling the building over night to reduce day time loading. Wrote 450 pages of what was wrong with the building, its design, the deficient ASHRAE standard, and lots of other problems. We studied the building for six months. Hundreds of people ordered the reports from the county. They established a protocol for similar investigations in the future. Bob Dear Colleagues:As I have the opportunity to assess actual ventilation performance in more buildings by reviewing carbon dioxide monitoring data,I'm finding more and more examples where the VAV boxes serving conference rooms do not go to their full open positionsdespite full occupancy conditions.This failure of the VAV approach to perform as intended results in ventilation deficiencies in these conference rooms,where even ASHRAE recommended ventilation minimums are not even being achieved.Has anyone else looked at this aspect of HVAC performance,and if so, are they finding similar results?Sincerely, W. Bearg, PE, CIHLife Energy Associateswww.LifeEnergyAssoc.com20 Darton StreetConcord, MA 01742 Re: Question about Icynene foam , While it is true that isocyanates are powerful sensitizers, the isocyanates actually used in the foam are in prepolymer form (several units of isocyanate bonded together, called part "A")and therefore not volatile. Residual amounts of monomeric isocyanate present in the prepolymer are supposed to be very low. The reactions between part A and part B (polyols) that create the polyurethane (PU)are over in seconds and all the isocyanate groups are reacted to urethanes. PU foams may have amine catalysts and in two cases I was involved with, the PU foam used had to be removed. I don't know why these had inappropriate amounts of catalyst, but the foams smelled like ammonia long after installation. I was around one PU foam installation and the odor around the truck was quite objectionable to me but the foam a few days after installation was odorless. All PU foams are derived from isocyanates; I believe the green foams contain a polyol (part that is derived from plant material. Wikepedia has a great explanation of the chemistry. May May Indoor Air Investigations LLC Tyngsborough, MA www.mayindoorair.com __________________________________________________________ > 2b. Re: Question about Icynene foam > Posted by: "sagefarmcomcast (DOT) net" sagefarmcomcast (DOT) net ieqdoc > Date: Thu Dec 24, 2009 11:36 am ((PST)) > > Jeff: > > Considering that these 2-component polyurethane spray foams include > an isocyanurate in one of the components, > > and isocyanurates are very powerful respiratory irritants, > > do you recommend some interval during and after application that the > sensitive individual not be at home? > > Even these newer "green" spray foams all seem to have isocyanurates as well. > > > > > Life Energy Associates > www.LifeEnergyAssoc.com > 20 Darton Street > Concord, MA 01742 > > > > All: > > In the past, I have often recommended open-celled Icynene foam, even > to clients with chemical sensitivities, and have not heard of any > problems. > > I believe that there are newer (greener?) foam formulations and I am > wondering if any of you have investigated any problem installations. > > If there were problems, was the cause determined? > > Thanks. > > May > May Indoor Air Investigations LLC > Tyngsborough, MA > www.mayindoorair.com > Quote
Guest guest Posted January 1, 2010 Report Posted January 1, 2010 , One of the main problems I have seen with VAV boxes delivering adequate ventilation is simply that the thermostats are set in the Automatic mode instead of the Fan On mode during occupied hours. Whether it's a conference room or a waiting room, I think CO2 demand based exhaust ventilation is a good idea provided that negative pressurization of the room or area doesn't create outside air infiltration problems -- even if it exhausts to a ceiling space or return duct. I recently saw a bathroom exhaust tied into a return duct. That was a bad idea. Steve Temes Dear Colleagues: As I have the opportunity to assess actual ventilation performance in more buildings by reviewing carbon dioxide monitoring data, I'm finding more and more examples where the VAV boxes serving conference rooms do not go to their full open positions despite full occupancy conditions. This failure of the VAV approach to perform as intended results in ventilation deficiencies in these conference rooms, where even ASHRAE recommended ventilation minimums are not even being achieved. Has anyone else looked at this aspect of HVAC performance, and if so, are they finding similar results? Sincerely, W. Bearg, PE, CIH Life Energy Associates www.LifeEnergyAssoc.com 20 Darton Street Concord, MA 01742 Quote
Guest guest Posted January 1, 2010 Report Posted January 1, 2010 One of the main problems I have seen with VAV boxes delivering adequate ventilation is simply that the thermostats are set in the Automatic mode instead of the Fan On mode during occupied hours. Correction: These are problems I have seen with heat pump thermostats, not VAV terminal thermostats. In VAV systems, occupants will often adjust the temperature setting to reduce drafts and noise caused by the fully open damper so that the air flow at the diffuser will be at its minimum rate. Then insufficient outside air gets to the occupied space regardless of the percentage of outside air in the available supply air. There is also less efficient mixing of supply air in the space at the lower flow rate. Steve Temes Quote
Recommended Posts
Join the conversation
You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.