Ultrafine Particle Counts (PTRAK CPC)

Rate this topic


Recommended Posts

Posted

I am currently working on IAQ investigation in which the ultrafine particle

counts (8,000 to 24,000 pt/cc) seems to be higher than expected for the

environment. The complaint (multiple asthma/respiratory) area is an office

environment in health care/clinical setting. The area is served by central HVAC

(VAV, Hot Water Reheat, Direct Steam Humidification, Ducted Returns), and with

2-stage filtration (MERV 8 and 12-14). Other Parameters: Carbon Dioxide

500-600ppm, Temperature 71-76°F, RH 30-40%, positive pressure relationship to

hallways and adjacent areas, no clear source(s) identified in immediate work

environment, and so far HVAC engineers have not reported anything unusual with

system.

Based on my experience and comparison with other similar environments particle

counts are typically around1000 to 5000 pt/cc. On few occasions over the last

few years have seen other areas with relatively short lived spikes in the

8,000-19,000 pt/cc range associated with vehicle exhaust migration or

copier/printers. But in this particular office the counts (data logging) have

been consistently elevated (12,000 to 16,500 pt/cc) for multiple hours over

several days at a time. After conducting particle counts for almost two weeks, I

did record a drop off in counts (1000 to 4000 pt/cc) for 1-2 days when weather

condition changed (Slightly warmer ~ 50°F and Rain). However, counts increased

back to 12,000 to 24,000 pt/cc) as soon as outside temperature and humidity/dew

point dropped in the last 2 days. I have also noted spikes of 2000-5000 pt/cc

over the room counts or backgrounds when readings taken inside supply duct just

before diffusers.

I realize this is lot of details, but with no outside or internal source clearly

noted so far, I am looking for feedback and thoughts on these counts. One

specific question: Anyone seen this similar pattern or counts associated with

humidification systems particularly direct steam? If so, anyone conducted

further analysis (i.e. water vapor, contaminants, steam additive,etc….) Given my

review of the literature (case reports, increasing research on potential health

effects from ultrafines) it would seem to me that we should follow-up and try

determine source and make attempt to control or eliminate. I would like add at

this point the engineers are reluctant to accept this may be problem or source

of the complaints and take any additional steps (i.e. turn off humidifier or

conduct systematic evaluation) Thanks for your thoughts and consideration on

this post.

Ron Howell, Industrial Hygienist

rjh134@...

Guest guest
Posted

Ron,

Based on your description of the situation, my first thought is that filter bypass is occurring. The system seems to be delivering good ventilation. If there is a correlation with indoor particle counts and outdoor conditions, proper filtration of outside air is what I would investigate first. Look at how well the filters fit in the filter rack.

I would also consider mineral impurities in the humidification water. Clean steam should not contain anything but water vapor. The steam nozzles in the ductwork should not look all gunked up with mineral residue.

I wouldn't rely on the engineers' observations. I would insist on having them show you the filters and the steam humidification nozzles. Your data suggest that the problem is inside the supply ductwork.

Steve Temes

I am currently working on IAQ investigation in which the ultrafine particle counts (8,000 to 24,000 pt/cc) seems to be higher than expected for the environment. The complaint (multiple asthma/respiratory) area is an office environment in health care/clinical setting. The area is served by central HVAC (VAV, Hot Water Reheat, Direct Steam Humidification, Ducted Returns), and with 2-stage filtration (MERV 8 and 12-14). Other Parameters: Carbon Dioxide 500-600ppm, Temperature 71-76°F, RH 30-40%, positive pressure relationship to hallways and adjacent areas, no clear source(s) identified in immediate work environment, and so far HVAC engineers have not reported anything unusual with system.

Based on my experience and comparison with other similar environments particle counts are typically around1000 to 5000 pt/cc. On few occasions over the last few years have seen other areas with relatively short lived spikes in the 8,000-19,000 pt/cc range associated with vehicle exhaust migration or copier/printers. But in this particular office the counts (data logging) have been consistently elevated (12,000 to 16,500 pt/cc) for multiple hours over several days at a time. After conducting particle counts for almost two weeks, I did record a drop off in counts (1000 to 4000 pt/cc) for 1-2 days when weather condition changed (Slightly warmer ~ 50°F and Rain). However, counts increased back to 12,000 to 24,000 pt/cc) as soon as outside temperature and humidity/dew point dropped in the last 2 days. I have also noted spikes of 2000-5000 pt/cc over the room counts or backgrounds when readings taken inside supply duct just before diffusers.

I realize this is lot of details, but with no outside or internal source clearly noted so far, I am looking for feedback and thoughts on these counts. One specific question: Anyone seen this similar pattern or counts associated with humidification systems particularly direct steam? If so, anyone conducted further analysis (i.e. water vapor, contaminants, steam additive,etc….) Given my review of the literature (case reports, increasing research on potential health effects from ultrafines) it would seem to me that we should follow-up and try determine source and make attempt to control or eliminate. I would like add at this point the engineers are reluctant to accept this may be problem or source of the complaints and take any additional steps (i.e. turn off humidifier or conduct systematic evaluation) Thanks for your thoughts and consideration on this post.

Ron Howell, Industrial Hygienist

rjh134@...

Guest guest
Posted

A few thoughts

yes, worth seeing if it could be the steam humidification. Is the steam treated? The anti-corrosives could be asthmagens. You can look at msds

is there correlation to outdoor levels? Do levels drop at nite? Could be leaky filters. By the way, the hospital office building I used to work in the typical indoor level was 20,000 (it was probably 40-60,000 p/ccoutside (Manhattan is high). We moved across the street to newly renovated buiding and the levels are 5,000. More efficient filters, I imagine.

One thing that would generate fine particles in a hospital would be cauterization or laser surgery or maybe aerosol therapy or diagnosis. You could see if any in same ventilation zone.

-----Original Message-----From: iequality [mailto:iequality ]On Behalf Of uncehsiaqSent: Saturday, February 27, 2010 9:42 AMTo: iequality Subject: Ultrafine Particle Counts (PTRAK CPC)

I am currently working on IAQ investigation in which the ultrafine particle counts (8,000 to 24,000 pt/cc) seems to be higher than expected for the environment. The complaint (multiple asthma/respiratory) area is an office environment in health care/clinical setting. The area is served by central HVAC (VAV, Hot Water Reheat, Direct Steam Humidification, Ducted Returns), and with 2-stage filtration (MERV 8 and 12-14). Other Parameters: Carbon Dioxide 500-600ppm, Temperature 71-76°F, RH 30-40%, positive pressure relationship to hallways and adjacent areas, no clear source(s) identified in immediate work environment, and so far HVAC engineers have not reported anything unusual with system.Based on my experience and comparison with other similar environments particle counts are typically around1000 to 5000 pt/cc. On few occasions over the last few years have seen other areas with relatively short lived spikes in the 8,000-19,000 pt/cc range associated with vehicle exhaust migration or copier/printers. But in this particular office the counts (data logging) have been consistently elevated (12,000 to 16,500 pt/cc) for multiple hours over several days at a time. After conducting particle counts for almost two weeks, I did record a drop off in counts (1000 to 4000 pt/cc) for 1-2 days when weather condition changed (Slightly warmer ~ 50°F and Rain). However, counts increased back to 12,000 to 24,000 pt/cc) as soon as outside temperature and humidity/dew point dropped in the last 2 days. I have also noted spikes of 2000-5000 pt/cc over the room counts or backgrounds when readings taken inside supply duct just before diffusers. I realize this is lot of details, but with no outside or internal source clearly noted so far, I am looking for feedback and thoughts on these counts. One specific question: Anyone seen this similar pattern or counts associated with humidification systems particularly direct steam? If so, anyone conducted further analysis (i.e. water vapor, contaminants, steam additive,etc….) Given my review of the literature (case reports, increasing research on potential health effects from ultrafines) it would seem to me that we should follow-up and try determine source and make attempt to control or eliminate. I would like add at this point the engineers are reluctant to accept this may be problem or source of the complaints and take any additional steps (i.e. turn off humidifier or conduct systematic evaluation) Thanks for your thoughts and consideration on this post.Ron Howell, Industrial Hygienist rjh134gmail

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...