Re: Current on metal water and gas pipes

Rate this topic


Recommended Posts

Guest guest
Posted

45 milligauss near the water pipe with the power off?

Could that be due to the electric meter being very close?

It's normal to have some neutral current, but 45 sounds

a little scary, like there could be an electrical problem.

The reverse polarity is also a bit scary. It sounds like

you know what you are doing, but if not have an electrician

look things over.

You can get a plumber to add a short section of plastic pex

pipe to the water, and a dielectric union for the gas. The

plumber may say it's not legal to not ground to metal pipes,

but plastic pipes are legal, so ...? Tell the plumber to be careful

and put a jumper wire around the cut. With that much current

he could get zapped otherwise. Then measure the voltage

after removing the wire. If it's more than a few volts it may

indicate some other problem, like a neighbor with a bad neutral?

If it's more than 10 volts I would keep the jumper wire there

until it's solved.

On Sat, Jun 12, 2010 at 8:29 AM, Barb <barb@...> wrote:

>

>

> In a few months I'll be moving into a house in Toronto that's throwing

> nasty magnetic fields off into one quadrant of the house. A preliminary

> inspection revealed things like: one electrical outlet with reverse

> polarity; some ungrounded outlets (the house is about 55 to 60 years old);

> even when the main power is shut off at the electrical box there is current

> on the water pipes (for sure detected just below the water meter and likely

> continuing through the basement ceiling's bulkhead) creating a 45 milligauss

> field (90 with the electricity on); stray current also on the gas pipes.

> It's my understanding that this magnetic field can be eliminated (for the

> most part), and even if it's being generated by a neighbouring home. I've

> started researching and I'm coming across a wide variety of recommendations

> and costs. It seems as though a number of items on the " to-do " list are

> relatively trivial but the stray current on the metal water and gas pipes is

> a bigger task. Does anyone have experience and/or input to share please?

>

> Thanks,

> Barb

>

>

>

Guest guest
Posted

Hi Barb,

An excellent resource for this situation is Karl Riley's book: Tracing EMFs in

Building Wiring and Grounding

http://www.lessemf.com/book8.html#530

It will help you (and/or your electrician and plumber) locate the various

sources of the problems and shows in detail how to fix them.

Emil

In a few months I'll be moving into a house in Toronto that's throwing nasty

magnetic fields off into one quadrant of the house. A preliminary inspection

revealed things like: one electrical outlet with reverse polarity; some

ungrounded outlets (the house is about 55 to 60 years old); even when the main

power is shut off at the electrical box there is current on the water pipes (for

sure detected just below the water meter and likely continuing through the

basement ceiling's bulkhead) creating a 45 milligauss field (90 with the

electricity on); stray current also on the gas pipes. It's my understanding that

this magnetic field can be eliminated (for the most part), and even if it's

being generated by a neighbouring home. I've started researching and I'm coming

across a wide variety of recommendations and costs. It seems as though a number

of items on the " to-do " list are relatively trivial but the stray current on the

metal water and gas pipes is a bigger task. Does anyone have experience and/or

input to share please? Thanks, Barb

Guest guest
Posted

Transformer on a pole at the foot of the driveway (not far). The circuitbreaker

box is perhaps 8 to 10 feet from the water meter. The SmartMeter is just a few

feet above the circuitbreaker box.

I would never do the work myself but thanks for saying I sound like I know what

I'm doing! I've educated myself and have experienced quite a lot re ES and/or

EHS; the surveying of the house was done by an EMF/RF expert. Sometimes I feel

like the more I know, the more I realize I don't know and thought I did.

For example, in the past, it seems to me that I heard a few times that a house's

electrical system is grounded to the metal water pipes... but really I don't

have any idea what that actually MEANS. Along with that, your ideas really make

sense to me, Bill, but then how the heck will the house's electrical system be

grounded?

Another example... umm, does a plumber also look after the gas pipes?

During the survey by the EMF/RF expert, a " regular " home inspector was also at

the premises. Although the regular home inspection doesn't test for current

and/or magnetic fields on metal water and gas pipes, the standard inspector said

that the amount of current found is indeed not acceptable by the building code.

He also noted that it's a very common scenario and that almost no one ever tests

for it and therefore no one enforces it either, but that the authorities wish it

didn't happen because it makes dangerous conditions for their employees and

tradespeople.

>

> >

> >

> > In a few months I'll be moving into a house in Toronto that's throwing

> > nasty magnetic fields off into one quadrant of the house. A preliminary

> > inspection revealed things like: one electrical outlet with reverse

> > polarity; some ungrounded outlets (the house is about 55 to 60 years old);

> > even when the main power is shut off at the electrical box there is current

> > on the water pipes (for sure detected just below the water meter and likely

> > continuing through the basement ceiling's bulkhead) creating a 45 milligauss

> > field (90 with the electricity on); stray current also on the gas pipes.

> > It's my understanding that this magnetic field can be eliminated (for the

> > most part), and even if it's being generated by a neighbouring home. I've

> > started researching and I'm coming across a wide variety of recommendations

> > and costs. It seems as though a number of items on the " to-do " list are

> > relatively trivial but the stray current on the metal water and gas pipes is

> > a bigger task. Does anyone have experience and/or input to share please?

> >

> > Thanks,

> > Barb

> >

> >

> >

>

>

>

Guest guest
Posted

Could it be possible that rectifying the individual issues such as the one

reversed polarity outlet or replacing the old ungrounded outlets with GFCIs

might stop the current from being on the metal pipes? Or is it so hefty at 45/90

milligauss that it must have an external source too? Or ...?

Thanks,

Barb

> >

> > >

> > >

> > > In a few months I'll be moving into a house in Toronto that's throwing

> > > nasty magnetic fields off into one quadrant of the house. A preliminary

> > > inspection revealed things like: one electrical outlet with reverse

> > > polarity; some ungrounded outlets (the house is about 55 to 60 years old);

> > > even when the main power is shut off at the electrical box there is

current

> > > on the water pipes (for sure detected just below the water meter and

likely

> > > continuing through the basement ceiling's bulkhead) creating a 45

milligauss

> > > field (90 with the electricity on); stray current also on the gas pipes.

> > > It's my understanding that this magnetic field can be eliminated (for the

> > > most part), and even if it's being generated by a neighbouring home. I've

> > > started researching and I'm coming across a wide variety of

recommendations

> > > and costs. It seems as though a number of items on the " to-do " list are

> > > relatively trivial but the stray current on the metal water and gas pipes

is

> > > a bigger task. Does anyone have experience and/or input to share please?

> > >

> > > Thanks,

> > > Barb

> > >

> > >

> > >

> >

> >

> >

Guest guest
Posted

Your ground wire from the electrical box at the house entrance should go to

a ground rod (copper rod 10' long driven into the ground). The wire should

be tight on the ground rod.

The ground wire in the electrical box should be tight under the ground screw

on the ground/neutral bar. The neutral wires on the bar should also be

tight. The screws on the circuit breakers should be tight. If you are

unfamiliar call an electrician as there can be 208-240 volts of power driven

by up to 200 amps.

If you still have current flowing to ground check all the plugs and light

switches in the house to be tight. If the problem persists disconnect all

the plugs in the house and if necessary turn off all the circuit breakers

until the problem goes away. Current on the ground wire is from a partial

short someplace. It could be very dangerous and should not be ignored.

Thanks,

Jim

_____

From: [mailto: ] On Behalf Of Barb

Sent: Saturday, June 12, 2010 8:58 PM

Subject: Re: Current on metal water and gas pipes

Transformer on a pole at the foot of the driveway (not far). The

circuitbreaker box is perhaps 8 to 10 feet from the water meter. The

SmartMeter is just a few feet above the circuitbreaker box.

I would never do the work myself but thanks for saying I sound like I know

what I'm doing! I've educated myself and have experienced quite a lot re ES

and/or EHS; the surveying of the house was done by an EMF/RF expert.

Sometimes I feel like the more I know, the more I realize I don't know and

thought I did.

For example, in the past, it seems to me that I heard a few times that a

house's electrical system is grounded to the metal water pipes... but really

I don't have any idea what that actually MEANS. Along with that, your ideas

really make sense to me, Bill, but then how the heck will the house's

electrical system be grounded?

Another example... umm, does a plumber also look after the gas pipes?

During the survey by the EMF/RF expert, a " regular " home inspector was also

at the premises. Although the regular home inspection doesn't test for

current and/or magnetic fields on metal water and gas pipes, the standard

inspector said that the amount of current found is indeed not acceptable by

the building code. He also noted that it's a very common scenario and that

almost no one ever tests for it and therefore no one enforces it either, but

that the authorities wish it didn't happen because it makes dangerous

conditions for their employees and tradespeople.

>

> >

> >

> > In a few months I'll be moving into a house in Toronto that's throwing

> > nasty magnetic fields off into one quadrant of the house. A preliminary

> > inspection revealed things like: one electrical outlet with reverse

> > polarity; some ungrounded outlets (the house is about 55 to 60 years

old);

> > even when the main power is shut off at the electrical box there is

current

> > on the water pipes (for sure detected just below the water meter and

likely

> > continuing through the basement ceiling's bulkhead) creating a 45

milligauss

> > field (90 with the electricity on); stray current also on the gas pipes.

> > It's my understanding that this magnetic field can be eliminated (for

the

> > most part), and even if it's being generated by a neighbouring home.

I've

> > started researching and I'm coming across a wide variety of

recommendations

> > and costs. It seems as though a number of items on the " to-do " list are

> > relatively trivial but the stray current on the metal water and gas

pipes is

> > a bigger task. Does anyone have experience and/or input to share please?

> >

> > Thanks,

> > Barb

> >

> >

> >

>

>

>

Guest guest
Posted

I'm confused. It's my understanding that the current is on the metal water pipes

and metal gas pipes NOT on the ground wire.

> >

> > >

> > >

> > > In a few months I'll be moving into a house in Toronto that's throwing

> > > nasty magnetic fields off into one quadrant of the house. A preliminary

> > > inspection revealed things like: one electrical outlet with reverse

> > > polarity; some ungrounded outlets (the house is about 55 to 60 years

> old);

> > > even when the main power is shut off at the electrical box there is

> current

> > > on the water pipes (for sure detected just below the water meter and

> likely

> > > continuing through the basement ceiling's bulkhead) creating a 45

> milligauss

> > > field (90 with the electricity on); stray current also on the gas pipes.

> > > It's my understanding that this magnetic field can be eliminated (for

> the

> > > most part), and even if it's being generated by a neighbouring home.

> I've

> > > started researching and I'm coming across a wide variety of

> recommendations

> > > and costs. It seems as though a number of items on the " to-do " list are

> > > relatively trivial but the stray current on the metal water and gas

> pipes is

> > > a bigger task. Does anyone have experience and/or input to share please?

> > >

> > > Thanks,

> > > Barb

> > >

> > >

> > >

> >

> >

> >

Guest guest
Posted

Some folks run the ground to the cold water pipes instead of a ground rod.

Never ground to a gas pipe. A ground rod is the best place. Any plastic in

the pipe runs will disable the ground and any stray voltage from a neighbors

pipe will come to your house.

Thanks,

Jim

_____

From: [mailto: ] On Behalf Of Barb

Sent: Sunday, June 13, 2010 11:15 AM

Subject: Re: Current on metal water and gas pipes

I'm confused. It's my understanding that the current is on the metal water

pipes and metal gas pipes NOT on the ground wire.

> >

> > >

> > >

> > > In a few months I'll be moving into a house in Toronto that's throwing

> > > nasty magnetic fields off into one quadrant of the house. A

preliminary

> > > inspection revealed things like: one electrical outlet with reverse

> > > polarity; some ungrounded outlets (the house is about 55 to 60 years

> old);

> > > even when the main power is shut off at the electrical box there is

> current

> > > on the water pipes (for sure detected just below the water meter and

> likely

> > > continuing through the basement ceiling's bulkhead) creating a 45

> milligauss

> > > field (90 with the electricity on); stray current also on the gas

pipes.

> > > It's my understanding that this magnetic field can be eliminated (for

> the

> > > most part), and even if it's being generated by a neighbouring home.

> I've

> > > started researching and I'm coming across a wide variety of

> recommendations

> > > and costs. It seems as though a number of items on the " to-do " list

are

> > > relatively trivial but the stray current on the metal water and gas

> pipes is

> > > a bigger task. Does anyone have experience and/or input to share

please?

> > >

> > > Thanks,

> > > Barb

> > >

> > >

> > >

> >

> >

> >

Guest guest
Posted

Sorry if I'm being dense... I'm confused again (or still!).

I think the current on the gas pipes is on a ground wire strung between the hot

water tank and the furnace (not certain about that though); it's not the main

ground wire of the house's electrical panel.

Jim, in your final sentence (directly below here), are the two parts of the

sentence separate?:

Part 1: Any plastic in the pipe runs will disable the ground

Part 2: Any stray voltage from a neighbors pipe will come to your house

What's the difference/benefit between a ground rod and a ground plate?

Thanks,

Barb

> > >

> > > >

> > > >

> > > > In a few months I'll be moving into a house in Toronto that's throwing

> > > > nasty magnetic fields off into one quadrant of the house. A

> preliminary

> > > > inspection revealed things like: one electrical outlet with reverse

> > > > polarity; some ungrounded outlets (the house is about 55 to 60 years

> > old);

> > > > even when the main power is shut off at the electrical box there is

> > current

> > > > on the water pipes (for sure detected just below the water meter and

> > likely

> > > > continuing through the basement ceiling's bulkhead) creating a 45

> > milligauss

> > > > field (90 with the electricity on); stray current also on the gas

> pipes.

> > > > It's my understanding that this magnetic field can be eliminated (for

> > the

> > > > most part), and even if it's being generated by a neighbouring home.

> > I've

> > > > started researching and I'm coming across a wide variety of

> > recommendations

> > > > and costs. It seems as though a number of items on the " to-do " list

> are

> > > > relatively trivial but the stray current on the metal water and gas

> > pipes is

> > > > a bigger task. Does anyone have experience and/or input to share

> please?

> > > >

> > > > Thanks,

> > > > Barb

> > > >

> > > >

> > > >

> > >

> > >

> > >

Guest guest
Posted

Ground rods are a piece of solid copper driven into the ground. I don't know

about ground plates. Folks have done crazy things with grounds. There should

only be one ground for your house and it shouldn't be a pipe. Use a copper

rod. I would get that ground wire between your furnace and hot water tank

fixed. Ground goes back to the main panel and then to the ground rod not to

another appliance.

Thanks,

Jim

_____

From: [mailto: ] On Behalf Of Barb

Sent: Sunday, June 13, 2010 9:02 PM

Subject: Re: Current on metal water and gas pipes

Sorry if I'm being dense... I'm confused again (or still!).

I think the current on the gas pipes is on a ground wire strung between the

hot water tank and the furnace (not certain about that though); it's not the

main ground wire of the house's electrical panel.

Jim, in your final sentence (directly below here), are the two parts of the

sentence separate?:

Part 1: Any plastic in the pipe runs will disable the ground

Part 2: Any stray voltage from a neighbors pipe will come to your house

What's the difference/benefit between a ground rod and a ground plate?

Thanks,

Barb

> > >

> > > >

> > > >

> > > > In a few months I'll be moving into a house in Toronto that's

throwing

> > > > nasty magnetic fields off into one quadrant of the house. A

> preliminary

> > > > inspection revealed things like: one electrical outlet with reverse

> > > > polarity; some ungrounded outlets (the house is about 55 to 60 years

> > old);

> > > > even when the main power is shut off at the electrical box there is

> > current

> > > > on the water pipes (for sure detected just below the water meter and

> > likely

> > > > continuing through the basement ceiling's bulkhead) creating a 45

> > milligauss

> > > > field (90 with the electricity on); stray current also on the gas

> pipes.

> > > > It's my understanding that this magnetic field can be eliminated

(for

> > the

> > > > most part), and even if it's being generated by a neighbouring home.

> > I've

> > > > started researching and I'm coming across a wide variety of

> > recommendations

> > > > and costs. It seems as though a number of items on the " to-do " list

> are

> > > > relatively trivial but the stray current on the metal water and gas

> > pipes is

> > > > a bigger task. Does anyone have experience and/or input to share

> please?

> > > >

> > > > Thanks,

> > > > Barb

> > > >

> > > >

> > > >

> > >

> > >

> > >

Guest guest
Posted

Bill, I've been reading this thread and as the EMF has been very high

checked my water pipes that come in from outside, it was very high. I

switched the electics off at the mains and it remained the same. The outlet

plugs in the kitchen were also high even with the electrics off.

Because of this I again got the Electricity Board out who tested all my

electrics and said they were okay, they're relatively new. The engineer's

conclusion was that it is radio waves.

I don't know if anyone else has noticed it but when I use my digital

(satellite) TV in the lounge it makes it much worse. In fact the entire

wall along that side of the house where my TV is plugged in registers

extremely high on my TriField meter. It's unbearable so I use my portable.

Now, although I've only had digital TV for around three years, I've had the

high levels of EMF since I believe the year 2000 at which time it caused

considerable personal damage which I recorded at the time. Just prior to

the beginning of all this electronic stuff the adjoining house next door,

although no-one was ever there, had a satellite dish set up outside his

house. I've always seen this as the onset of what came.

But there are so many problems like for instance today I sat watching my

portable (which doesn't carry the high levels of EMF that my digital one

does), and after hammering on the adjoining wall and interference lines

began across my TV screen, and the high suges of EMF then began throughout

the house. My outside front hedge leading from the pavement to the outside

wall of my home, beneath which the utilities are is almost dead now and

several years ago it was a thick, thriving, privet hedge.

My experience is that there are several issues at work here, and they're all

electricity of one kind or another. I'm not sure if I can change the levels

of EMF on my water pipes which the other day left my legs vibrating when I

was in the kitchen. It leaves me very tired. I'm thankful for my faith

which has given me so much including joy and peace in the worst of it.

Also, I'm able to rest at different times throughout the day, in fact when

it's bad I can't keep awake.

The thing is if I resolved the EMF I'm not sure it would stop the microwaves

that I am subjected to both in my bed and other parts of my home? These did

so much damage when it first began in the year 2000, before I learned to

protect myself with sheilding. I don't believe there is any protection from

the EMF.

Re: Current on metal water and gas pipes

> 45 milligauss near the water pipe with the power off?

> Could that be due to the electric meter being very close?

>

> It's normal to have some neutral current, but 45 sounds

> a little scary, like there could be an electrical problem.

> The reverse polarity is also a bit scary. It sounds like

> you know what you are doing, but if not have an electrician

> look things over.

>

> You can get a plumber to add a short section of plastic pex

> pipe to the water, and a dielectric union for the gas. The

> plumber may say it's not legal to not ground to metal pipes,

> but plastic pipes are legal, so ...? Tell the plumber to be careful

> and put a jumper wire around the cut. With that much current

> he could get zapped otherwise. Then measure the voltage

> after removing the wire. If it's more than a few volts it may

> indicate some other problem, like a neighbor with a bad neutral?

> If it's more than 10 volts I would keep the jumper wire there

> until it's solved.

>

>

> On Sat, Jun 12, 2010 at 8:29 AM, Barb <barb@...> wrote:

>

> >

> >

> > In a few months I'll be moving into a house in Toronto that's throwing

> > nasty magnetic fields off into one quadrant of the house. A preliminary

> > inspection revealed things like: one electrical outlet with reverse

> > polarity; some ungrounded outlets (the house is about 55 to 60 years

old);

> > even when the main power is shut off at the electrical box there is

current

> > on the water pipes (for sure detected just below the water meter and

likely

> > continuing through the basement ceiling's bulkhead) creating a 45

milligauss

> > field (90 with the electricity on); stray current also on the gas pipes.

> > It's my understanding that this magnetic field can be eliminated (for

the

> > most part), and even if it's being generated by a neighbouring home.

I've

> > started researching and I'm coming across a wide variety of

recommendations

> > and costs. It seems as though a number of items on the " to-do " list are

> > relatively trivial but the stray current on the metal water and gas

pipes is

> > a bigger task. Does anyone have experience and/or input to share please?

> >

> > Thanks,

> > Barb

> >

> >

> >

>

>

>

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...