It's been awhile since I asked this question, and it is about time to

see if we have any new information. Has anyone lately done any

analysis on duct dust, the dust that has accumulated in ductwork? If

so, what did you discover? If you can, please delineate whether the

dust came from the return or supply air ducts. Thanks. Matt

************************************************************

K. Klein, PE ME, MBA

Matt:

I don't know about "we" having new information or the findings being a discovery, but here is an excerpt from a report of a study in which I had dust samples analyzed microscopically to determine the constituent fibrous and particulate components for the purpose of confirming that the source of the settled dust in the room was the return duct (yes, high velocity air flow OUT of the return duct carried a huge amount of dust with it):

Microscopic analysis showed that the settled dust sample from (the room) was about 60% fibrous materials and 40% particulate. Major fibrous components were cellulose, cotton and synthetic fibers in approximately equal amounts. About 25% of the fibers were dyed primarily blue, green and red. Minor fibrous components (< 5% of the total sample) were wool, fiberglass and other fibers. Fiberglass represented about one percent of the sample.

In the analysis of the dust collected from the return duct in the ceiling of Room 211 it was determined that about 50% of the sample was fibrous material and 50% was particulate. Major and minor fiber types were similar to those in the settled dust sample. Fiber composition was about 20% cellulose, 15% cotton, 10% synthetics, 3% wool/others and 2% fiberglass.

The fiberglass duct liner sample contained about 85% fibrous material and 15% particulate. Nearly all of the fibrous content was fiberglass.

I hope that helps,

Steve Temes

Link to comment
Share on other sites

Matt,

I have found more dust in the returns then in the supply on most projects. Although I have ran into projects that had supplies not properly installed or torn down (more evident in crawlspace ducting) where there was a magnitude greater by 10 times.

As with all other IEQ investigations I have done, there seems to be no hard and fast rules when it comes to ducts.

Perhaps someone from NADCA has better statistics.... :-)

Larkin

Duct Dust

It's been awhile since I asked this question, and it is about time to see if we have any new information. Has anyone lately done any analysis on duct dust, the dust that has accumulated in ductwork? If so, what did you discover? If you can, please delineate whether the dust came from the return or supply air ducts. Thanks. Matt************ ********* ********* ********* ********* ********* *** K. Klein, PE ME, MBAIndoor Air Quality Solutions, Inc.2523 SR 133Bethel, OH 45106-0007VOICE: FAX: (with notice)E-mail: mkklein68@roadrunne r.com************ ********* ********* ********* ********* ********* ***

Everyone is raving about the all-new Yahoo! Mail beta.

Link to comment
Share on other sites

Matt,

On the return side, which in residential systems is always much dirtier than

the supplies,most of the dust is house dust: skin scales, lint and pet

dander. I have also found dust mites foraging in returns.

Mold will grow in the dust if it gets wet (people often put boots to dry

over floor grilles ) or if the dust is in a cool damp location (e.g. contact

with concrete or in a crawl space.)

Most of the debris in supplies has fallen in. I have found marbles and balls

and moldy dog food and cheerios.

One interesting phenomenon occurs in horizontal round ducts (at basement

ceilings) and can often be seen with a mirror at a first-floor register

boot. Only the lower half of the duct is coated with a very fine layer of

dust.

I believe that this dust is deposited after the blower shuts down. Hot air

flows out of the system by convection at the top of the duct. Colder house

air (which is denser) flows into the system at the lower half of the duct,

depositing the dust at only the lower half.

Relatively recent additions to duct dust are the 5-10 micron colored spheres

from laser printers (these are the primary paint colors). Sometimes there

are large numbers of spray paint spheres that get trapped on the surface of

fiberglass-lined ducts. These spheres come in a large range of sizes (3-25

microns) and are full of pigment particles. The spheres are opaque (black)

with transmitted light, and white using reflected light.

Spider silk and insect droppings can be a large component in duct dust as

well.

C. May, M.A., CIAQP

May Indoor Air Investigations LLC

1522 Cambridge Street

Cambridge, MA 02139

www.mayindoorair.com

www.myhouseiskillingme.com

Klein writes:

> It's been awhile since I asked this question, and it is about time to

> see if we have any new information. Has anyone lately done any

> analysis on duct dust, the dust that has accumulated in ductwork? If

> so, what did you discover? If you can, please delineate whether the

> dust came from the return or supply air ducts. Thanks. Matt

>

> ************************************************************

> K. Klein, PE ME, MBA

> Indoor Air Quality Solutions, Inc.

> 2523 SR 133

> Bethel, OH 45106-0007

> VOICE:

> FAX: (with notice)

> E-mail: mkklein68@...

Link to comment
Share on other sites

Matt,

This is an indirect answer to your question, but I have routinely sampled

the air filter in the HVAC system in residential settings. This of course,

is located at the end of the return air stream. I take a " composite " swab

sample of both sides of the filter to equal a total surface area samples

of 100 cm2.

My reasons for doing so are that these samples often present a good

" picture in time " , and can be particularly interesting if you know

approximately how long the filter has been in place, as well as in

comparing the fungi and bacteria to other air and surface sample results

from the structure.

Obviously, a separate set of colonies can develop on the filter itself,

particularly if it is very dirty/hasn't been changed in a long while so it's

not always useful, but often is. In a situation with an extremely dirty

filter, I will usually opt to not collect a sample from it.

It also helps tremendously if the system is forced air (for the benefit of

contractors who are consultant wannabes).

On occasion, I've also sampled the filter medium in portable room air

filters as well for the same reasons.

Sometimes the results are more helpful than others, but that's how it

goes when you're piecing a puzzle together. Some pieces fit, and some

don't.

Cheers,

Chuck Reaney, CIAQetc & PIE (political incorrectness expert)

To: IEQ List <iequality >

Date sent: Tue, 28 Nov 2006 15:29:10 -0500

Subject: Duct Dust

Send reply to: iequality

[ Double-click this line for list subscription options ]

It's been awhile since I asked this question, and it is about time to

see if we have any new information. Has anyone lately done any

analysis on duct dust, the dust that has accumulated in ductwork? If

so, what did you discover? If you can, please delineate whether the

dust came from the return or supply air ducts. Thanks. Matt

************************************************************

K. Klein, PE ME, MBA

Indoor Air Quality Solutions, Inc.

2523 SR 133

Bethel, OH 45106-0007

VOICE:

FAX: (with notice)

E-mail: mkklein68@...

************************************************************

FAIR USE NOTICE:

This site contains copyrighted material the use of which has not

always been specifically authorized by the copyright owner. We are

making such material available in our efforts to advance understanding

of environmental, political, human rights, economic, democracy,

scientific, and social justice issues, etc. We believe this

constitutes a 'fair use' of any such copyrighted material as provided

for in section 107 of the US Copyright Law. In accordance with Title

17 U.S.C. Section 107, the material on this site is distributed

without profit to those who have expressed a prior interest in

receiving the included information for research and educational

purposes. For more information go to:

http://www.law.cornell.edu/uscode/17/107.shtml. If you wish to use

copyrighted material from this site for purposes of your own that go

beyond 'fair use', you must obtain permission from the copyright

owner.

Link to comment
Share on other sites

My suggestions for sampling mold on (in) air filters (1) Heavy dust load (loose dust on surface): micro-vac the surface on a measured area and then cut the entire measured area * Make sure your lab knows what to do with them (2) Light dust load (no loose dust on surface): cut a bulk piece (micro-vac optional) Swabs don't work very well on collecting subsurface mold. Wei Tang QLab Chuck Reaney wrote: Matt,This is an indirect answer to your question, but I have routinely sampled the air filter in the HVAC system in residential settings. This of course, is located at the end of the return air stream. I take a "composite" swab sample of both sides of the filter to equal a total surface area samples of 100 cm2.My reasons for doing so are that these samples often present a good "picture in time", and can be particularly interesting if you know approximately how long the filter has been in place, as well as in comparing the fungi and bacteria to other air and surface sample results from the structure.Obviously, a separate set of colonies can develop on the filter itself, particularly if it is very dirty/hasn't been changed in a long while so it's not always useful, but often is. In a situation with an extremely dirty filter, I will usually opt

to not collect a sample from it.It also helps tremendously if the system is forced air (for the benefit of contractors who are consultant wannabes).On occasion, I've also sampled the filter medium in portable room air filters as well for the same reasons.Sometimes the results are more helpful than others, but that's how it goes when you're piecing a puzzle together. Some pieces fit, and some don't.Cheers,Chuck Reaney, CIAQetc & PIE (political incorrectness expert)To: IEQ List <iequality >From: Klein <mkklein68roadrunner>Date sent: Tue, 28 Nov 2006 15:29:10 -0500Subject: Duct DustSend reply to: iequality [

Double-click this line for list subscription options ] It's been awhile since I asked this question, and it is about time tosee if we have any new information. Has anyone lately done anyanalysis on duct dust, the dust that has accumulated in ductwork? Ifso, what did you discover? If you can, please delineate whether thedust came from the return or supply air ducts. Thanks. Matt************************************************************ K. Klein, PE ME, MBAIndoor Air Quality Solutions, Inc.2523 SR 133Bethel, OH 45106-0007VOICE: FAX: (with notice)E-mail: mkklein68roadrunner************************************************************ FAIR USE NOTICE:This site contains copyrighted material the use of which has notalways been specifically

authorized by the copyright owner. We aremaking such material available in our efforts to advance understandingof environmental, political, human rights, economic, democracy,scientific, and social justice issues, etc. We believe thisconstitutes a 'fair use' of any such copyrighted material as providedfor in section 107 of the US Copyright Law. In accordance with Title17 U.S.C. Section 107, the material on this site is distributedwithout profit to those who have expressed a prior interest inreceiving the included information for research and educationalpurposes. For more information go to:http://www.law.cornell.edu/uscode/17/107.shtml. If you wish to usecopyrighted material from this site for purposes of your own that gobeyond 'fair use', you must obtain permission from the copyrightowner. Yahoo! Groups

Links QLab5 DriveCherry Hill, NJ 08003www.QLabUSA.com

Link to comment
Share on other sites

Thanks, Wei. I'll keep that in mind.

Chuck

To: iequality

Date sent: Wed, 29 Nov 2006 13:30:45 -0800 (PST)

Subject: Re: Duct Dust

Send reply to: iequality

My suggestions for sampling mold on (in) air filters

(1) Heavy dust load (loose dust on surface): micro-vac the surface

on a measured area and then cut the entire measured area * Make

sure

your lab knows what to do with them

(2) Light dust load (no loose dust on surface): cut a bulk piece

(micro-vac optional)

Swabs don't work very well on collecting subsurface mold.

Wei Tang

QLab

Chuck Reaney wrote:

Matt,

This is an indirect answer to your question, but I have routinely

sampled the air filter in the HVAC system in residential settings.

This of course, is located at the end of the return air stream. I take

a " composite " swab sample of both sides of the filter to equal a total

surface area samples of 100 cm2.

My reasons for doing so are that these samples often present a good

" picture in time " , and can be particularly interesting if you know

approximately how long the filter has been in place, as well as in

comparing the fungi and bacteria to other air and surface sample

results from the structure.

Obviously, a separate set of colonies can develop on the filter

itself, particularly if it is very dirty/hasn't been changed in a long

while so it's not always useful, but often is. In a situation with an

extremely dirty filter, I will usually opt to not collect a sample

from it.

It also helps tremendously if the system is forced air (for the

benefit of contractors who are consultant wannabes).

On occasion, I've also sampled the filter medium in portable room air

filters as well for the same reasons.

Sometimes the results are more helpful than others, but that's how it

goes when you're piecing a puzzle together. Some pieces fit, and some

don't.

Cheers,

Chuck Reaney, CIAQetc & PIE (political incorrectness expert)

To: IEQ List <iequality >

Date sent: Tue, 28 Nov 2006 15:29:10 -0500

Subject: Duct Dust

Send reply to: iequality

[ Double-click this line for list subscription options ]

It's been awhile since I asked this question, and it is about time to

see if we have any new information. Has anyone lately done any

analysis on duct dust, the dust that has accumulated in ductwork? If

so, what did you discover? If you can, please delineate whether the

dust came from the return or supply air ducts. Thanks. Matt

************************************************************

K. Klein, PE ME, MBA

Indoor Air Quality Solutions, Inc.

2523 SR 133

Bethel, OH 45106-0007

VOICE:

FAX: (with notice)

E-mail: mkklein68@...

************************************************************

FAIR USE NOTICE:

This site contains copyrighted material the use of which has not

always been specifically authorized by the copyright owner. We are

making such material available in our efforts to advance understanding

of environmental, political, human rights, economic, democracy,

scientific, and social justice issues, etc. We believe this

constitutes a 'fair use' of any such copyrighted material as provided

for in section 107 of the US Copyright Law. In accordance with Title

17 U.S.C. Section 107, the material on this site is distributed

without profit to those who have expressed a prior interest in

receiving the included information for research and educational

purposes. For more information go to:

http://www.law.cornell.edu/uscode/17/107.shtml. If you wish to use

copyrighted material from this site for purposes of your own that go

beyond 'fair use', you must obtain permission from the copyright

owner.

Link to comment
Share on other sites

Thank you, Sherryl.

From: optimal@...

To: iequality , iequality

Copies to: " Chuck Reaney "

Subject: Re: Duct Dust

Date sent: Wed, 29 Nov 2006 19:26:31 +0000

Chuck - Talk with your lab. They may prefer and be able to give you

more information if you send a sample of the filter rather than take a

swab. Sherryl Schultz OPTIMAL@...

Link to comment
Share on other sites

Chuck, You are very welcome. BTW, did you tell us the reference where you get your PRV (clearance) criteria for surface mold? I am sorry that I didn't read all the posts. Wei Tang QLabChuck Reaney wrote: Thanks, Wei. I'll keep that in mind.ChuckTo: iequality From: Wei Tang <wtangQLABusa>Date sent: Wed, 29 Nov 2006 13:30:45 -0800 (PST)Subject: Re: Duct DustSend reply to: iequality My suggestions for sampling mold on (in) air filters(1) Heavy dust load (loose dust on surface): micro-vac the surfaceon a measured area and then cut the entire measured area * Make sureyour lab knows what to do with them(2) Light dust load (no loose dust on surface): cut a bulk piece(micro-vac optional)Swabs don't work very well on collecting subsurface mold. Wei TangQLabChuck Reaney <creaneyicdc> wrote:Matt,This is an indirect answer to your question, but I have routinelysampled the air filter in the HVAC system in residential settings.This of course, is located at the end of the

return air stream. I takea "composite" swab sample of both sides of the filter to equal a totalsurface area samples of 100 cm2.My reasons for doing so are that these samples often present a good"picture in time", and can be particularly interesting if you knowapproximately how long the filter has been in place, as well as incomparing the fungi and bacteria to other air and surface sampleresults from the structure.Obviously, a separate set of colonies can develop on the filteritself, particularly if it is very dirty/hasn't been changed in a longwhile so it's not always useful, but often is. In a situation with anextremely dirty filter, I will usually opt to not collect a samplefrom it.It also helps tremendously if the system is forced air (for thebenefit of contractors who are consultant wannabes).On occasion, I've also sampled the filter medium in portable room airfilters as well for the same

reasons.Sometimes the results are more helpful than others, but that's how itgoes when you're piecing a puzzle together. Some pieces fit, and somedon't.Cheers,Chuck Reaney, CIAQetc & PIE (political incorrectness expert)To: IEQ List <iequality >From: Klein <mkklein68roadrunner>Date sent: Tue, 28 Nov 2006 15:29:10 -0500Subject: Duct DustSend reply to: iequality [ Double-click this line for list subscription options ] It's been awhile since I asked this question, and it is about time tosee if we have any new information. Has anyone lately done anyanalysis on duct dust, the dust that has accumulated in ductwork?

Ifso, what did you discover? If you can, please delineate whether thedust came from the return or supply air ducts. Thanks. Matt************************************************************ K. Klein, PE ME, MBAIndoor Air Quality Solutions, Inc.2523 SR 133Bethel, OH 45106-0007VOICE: FAX: (with notice)E-mail: mkklein68roadrunner************************************************************ FAIR USE NOTICE:This site contains copyrighted material the use of which has notalways been specifically authorized by the copyright owner. We aremaking such material available in our efforts to advance understandingof environmental, political, human rights, economic, democracy,scientific, and social justice issues, etc. We believe thisconstitutes a 'fair use' of

any such copyrighted material as providedfor in section 107 of the US Copyright Law. In accordance with Title17 U.S.C. Section 107, the material on this site is distributedwithout profit to those who have expressed a prior interest inreceiving the included information for research and educationalpurposes. For more information go to:http://www.law.cornell.edu/uscode/17/107.shtml. If you wish to usecopyrighted material from this site for purposes of your own that gobeyond 'fair use', you must obtain permission from the copyrightowner.

Link to comment
Share on other sites

Chuck:

You've peaked my interest. I am very surprised that sampling a filter

(with the exception of a filter that is relatively new) would give any

useful results. On culturables don't you get waaaay too many colonies

to make heads or tails? And on optical microscopy samples, isn't

there too much debris for an adequate reading?

However, you've indicated that you do this with some regularity, so I

have to assume you have been getting some data that makes sense. If

possible, could you email me some of your lab reports from such

samples to clk@...?

Thanks.

Cassidy Kuchenbecker

>

> To: IEQ List <iequality >

>

> Date sent: Tue, 28 Nov 2006 15:29:10 -0500

> Subject: Duct Dust

> Send reply to: iequality

>

> [ Double-click this line for list subscription options ]

>

> It's been awhile since I asked this question, and it is about time to

> see if we have any new information. Has anyone lately done any

> analysis on duct dust, the dust that has accumulated in ductwork? If

> so, what did you discover? If you can, please delineate whether the

> dust came from the return or supply air ducts. Thanks. Matt

>

> ************************************************************

> K. Klein, PE ME, MBA

> Indoor Air Quality Solutions, Inc.

> 2523 SR 133

> Bethel, OH 45106-0007

> VOICE:

> FAX: (with notice)

> E-mail: mkklein68@...

> ************************************************************

>

> FAIR USE NOTICE:

>

> This site contains copyrighted material the use of which has not

> always been specifically authorized by the copyright owner. We are

> making such material available in our efforts to advance understanding

> of environmental, political, human rights, economic, democracy,

> scientific, and social justice issues, etc. We believe this

> constitutes a 'fair use' of any such copyrighted material as provided

> for in section 107 of the US Copyright Law. In accordance with Title

> 17 U.S.C. Section 107, the material on this site is distributed

> without profit to those who have expressed a prior interest in

> receiving the included information for research and educational

> purposes. For more information go to:

> http://www.law.cornell.edu/uscode/17/107.shtml. If you wish to use

> copyrighted material from this site for purposes of your own that go

> beyond 'fair use', you must obtain permission from the copyright

> owner.

Link to comment
Share on other sites

Cassidy:

I very often sample return air filters and supply air plenums. I

consider the filter to offer the possibility of a long-term composite

sample and therefore to be representative of material that has been

present in indoor air for a prolonged period of time. Room HEPA filters

are good for the same reason. I usually have both spore counts and

culturable fungi analyzed. The absolute numbers are usually low by both

methods, although dust may hide some of the spores. The relative

viability (CFU/counts) is usually low, because of the low relative

humidity of the air passing through the filter, unless there is a source

of water affecting the return air plenum. Sometimes I get information

that was not apparent from air samples but that may reflect source samples.

I sample supply air plenums for evidence of water damage and mold growth

from condensate backup, carryover, or other mechanisms. This allows an

evaluation of the AHU and supply air system as a source for fungal

contaminants in the indoor environment. It also allows evaluation of

microbial carryover from indoor environmental contamination (mold and

bacteria from water and sewage). I usually do this by cutting a wedge

from the ductboard plenum and then cutting a thin slice from the inside

surface and submitting that as a bulk sample. I also sometimes use swabs

and sometimes micro-vac samples. If the plenum is not readily available

or if it is metal, I smay sample supply air ducts and boots at

registers, or I may open the AHU and sample the blower, the evaporator

coil, or inside surfaces of the compartment, using swabs. This has

worked in two recent cases to identify how far into which air handling

systems sewage organisms progressed following sewage backup incidents.

Don Schaezler, Ph.D., P.E., CIH

ETC Information Services, LLC

Cibolo, Texas

Cassidy Kuchenbecker wrote:

>

>

> Chuck:

>

> You've peaked my interest. I am very surprised that sampling a filter

> (with the exception of a filter that is relatively new) would give any

> useful results. On culturables don't you get waaaay too many colonies

> to make heads or tails? And on optical microscopy samples, isn't

> there too much debris for an adequate reading?

>

> However, you've indicated that you do this with some regularity, so I

> have to assume you have been getting some data that makes sense. If

> possible, could you email me some of your lab reports from such

> samples to clk@...

> <mailto:clk%40michaelsengineering.com>?

>

> Thanks.

>

> Cassidy Kuchenbecker

>

>

> >

> > To: IEQ List <iequality

> <mailto:iequality%40yahoogroups.com>>

> >

> > Date sent: Tue, 28 Nov 2006 15:29:10 -0500

> > Subject: Duct Dust

> > Send reply to: iequality

> <mailto:iequality%40yahoogroups.com>

> >

> > [ Double-click this line for list subscription options ]

> >

> > It's been awhile since I asked this question, and it is about time to

> > see if we have any new information. Has anyone lately done any

> > analysis on duct dust, the dust that has accumulated in ductwork? If

> > so, what did you discover? If you can, please delineate whether the

> > dust came from the return or supply air ducts. Thanks. Matt

> >

> > ************************************************************

> > K. Klein, PE ME, MBA

> > Indoor Air Quality Solutions, Inc.

> > 2523 SR 133

> > Bethel, OH 45106-0007

> > VOICE:

> > FAX: (with notice)

> > E-mail: mkklein68@...

> > ************************************************************

> >

> > FAIR USE NOTICE:

> >

> > This site contains copyrighted material the use of which has not

> > always been specifically authorized by the copyright owner. We are

> > making such material available in our efforts to advance understanding

> > of environmental, political, human rights, economic, democracy,

> > scientific, and social justice issues, etc. We believe this

> > constitutes a 'fair use' of any such copyrighted material as provided

> > for in section 107 of the US Copyright Law. In accordance with Title

> > 17 U.S.C. Section 107, the material on this site is distributed

> > without profit to those who have expressed a prior interest in

> > receiving the included information for research and educational

> > purposes. For more information go to:

> > http://www.law.cornell.edu/uscode/17/107.shtml.

> <http://www.law.cornell.edu/uscode/17/107.shtml.> If you wish to use

> > copyrighted material from this site for purposes of your own that go

> > beyond 'fair use', you must obtain permission from the copyright

> > owner.

Link to comment
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...