Ian,

Right you are. However, there is also a default value of 17 cfm/person based on an assumed occupant density of 5 persons/1000 s/f for office spaces. I usually say "should be about 15-20 cfm/person" when I perform ventilation assessments using CO2 measurements (not for engineering design purposes). If levels are elevated, further assessment of the HVAC system design and operation is indicated (unless I can make the levels come down by switching the T-stat to "fan on").

Steve Temes

In some recent posts over the last few weeks I've seen some outdated

numbers being thrown around for ASHRAE ventilation rates.

ASHRAE no longer has a 20 cfm/person ventilation rate for office

spaces. The rate is now broken down into cfm/person and cfm/square

foot. The current standard is only 5 cfm/person and 0.06 cfm/SF.

You add the two together. See ASHRAE 62.1-2004

When dealing with homes, it's best to reference ASHRAE Standard 62.2-

2004. Their recommendations for a standard 2000 SF home with 4

bedrooms is 57.5 cfm of outdoor air if you do the math.

These have been around for a while so everyone should update their

libraries.

Just bein' an engineer!

Ian Cull, PE, CIE

Link to comment
Share on other sites

In some recent posts over the last few weeks I've seen some outdated

numbers being thrown around for ASHRAE ventilation rates.

ASHRAE no longer has a 20 cfm/person ventilation rate for office

spaces. The rate is now broken down into cfm/person and cfm/square

foot. The current standard is only 5 cfm/person and 0.06 cfm/SF.

You add the two together. See ASHRAE 62.1-2004

When dealing with homes, it's best to reference ASHRAE Standard 62.2-

2004. Their recommendations for a standard 2000 SF home with 4

bedrooms is 57.5 cfm of outdoor air if you do the math.

These have been around for a while so everyone should update their

libraries.

Just bein' an engineer!

Ian Cull, PE, CIE

Chelsea Training

www.invironment.com

www.LabComparisons.com

Link to comment
Share on other sites

Dear Ian:

If the modification to the ASHRAE minimum recommended ventilation rate to

achieve " acceptable " IAQ now includes a term that is based on square footage of

the space being ventilated, I ask if the intent of this change is to address the

air contaminants off-gassing from the furnishings, and since this off-gassing

occurs on a 24/7 basis, should the ventilation minimum recommendation be

provided on a 24/7 basis as well?

What I'm seeing is aggressive ventilation rates being provided during peak

occupancy, on the order of 24 cfm person of outdoor air delivered. But thev

limited hours of operation of this ventilation provided in a tight building

leaves a residual of bioeffluents, and presumably air contaminants off-gassed

during the overnight interval, that persist until occupancy the next morning.

In terms of good engineering practice, shouldn't a complete flushout of the

previous day's bioeffluents be achieved overnight, so the building's air doesn't

seem stale upon reentry by people the next day?

Does ASHRAE deal with this issue?

Sincerely,

W. Bearg, PE, CIH

Building Scientist

Concord, MA

--

Director of IAQ Programs

AIRxpert Systems, Inc.

www.AIRxpert.com

-------------- Original message ----------------------

In some recent posts over the last few weeks I've seen some outdated

numbers being thrown around for ASHRAE ventilation rates.

ASHRAE no longer has a 20 cfm/person ventilation rate for office

spaces. The rate is now broken down into cfm/person and cfm/square

foot. The current standard is only 5 cfm/person and 0.06 cfm/SF.

You add the two together. See ASHRAE 62.1-2004

When dealing with homes, it's best to reference ASHRAE Standard 62.2-

2004. Their recommendations for a standard 2000 SF home with 4

bedrooms is 57.5 cfm of outdoor air if you do the math.

These have been around for a while so everyone should update their

libraries.

Just bein' an engineer!

Ian Cull, PE, CIE

Chelsea Training

www.invironment.com

www.LabComparisons.com

Link to comment
Share on other sites

Building codes (IBC) still use 20 CFM as does the ACCA/ANSI Manual J design

criteria.

Tony

...........................................................................

" Tony " Havics, CHMM, CIH, PE

pH2, LLC

PO Box 34140

Indianapolis, IN 46234

cell

90% of Risk Management is knowing where to place the decimal point...any

consultant can give you the other 10%â„ 

This message is from pH2. This message and any attachments may contain legally

privileged or confidential information, and are intended only for the individual

or entity identified above as the addressee. If you are not the addressee, or if

this message has been addressed to you in error, you are not authorized to read,

copy, or distribute this message and any attachments, and we ask that you please

delete this message and attachments (including all copies) and notify the sender

by return e-mail or by phone at . Delivery of this message and any

attachments to any person other than the intended recipient(s) is not intended

in any way to waive confidentiality or a privilege. All personal messages

express views only of the sender, which are not to be attributed to pH2 and may

not be copied or distributed without this statement.

ASHRAE Ventilation Rates

In some recent posts over the last few weeks I've seen some outdated

numbers being thrown around for ASHRAE ventilation rates.

ASHRAE no longer has a 20 cfm/person ventilation rate for office

spaces. The rate is now broken down into cfm/person and cfm/square

foot. The current standard is only 5 cfm/person and 0.06 cfm/SF.

You add the two together. See ASHRAE 62.1-2004

When dealing with homes, it's best to reference ASHRAE Standard 62.2- 2004.

Their recommendations for a standard 2000 SF home with 4

bedrooms is 57.5 cfm of outdoor air if you do the math.

These have been around for a while so everyone should update their

libraries.

Just bein' an engineer!

Ian Cull, PE, CIE

Chelsea Training

www.invironment.com

www.LabComparisons.com

FAIR USE NOTICE:

This site contains copyrighted material the use of which has not always been

specifically authorized by the copyright owner. We are making such material

available in our efforts to advance understanding of environmental, political,

human rights, economic, democracy, scientific, and social justice issues, etc.

We believe this constitutes a 'fair use' of any such copyrighted material as

provided for in section 107 of the US Copyright Law. In accordance with Title 17

U.S.C. Section 107, the material on this site is distributed without profit to

those who have expressed a prior interest in receiving the included information

for research and educational purposes. For more information go to:

http://www.law.cornell.edu/uscode/17/107.shtml. If you wish to use copyrighted

material from this site for purposes of your own that go beyond 'fair use', you

must obtain permission from the copyright owner.

Link to comment
Share on other sites

,

My understanding is that the cfm/square foot in the new ASHRAE Std.

62.1-2004 is indeed to address the building's contribution to

unacceptable IAQ. This is a huge improvement on the previous

standard that only considers the human contribution.

You make a great point that I didn't consider. The human

contribution only happens when the space is occupied, and when it's

occupied, the outdoor air is being brought in. There may be

little/no ventilation to deal with the building's contribution at

night.

To my knowledge, ASHRAE doesn't address the night set back issue.

Just to be safe, I did a word search on " night " and " set back " on my

electronic copy of 62.1. Not a single word came up.

To add to the problems of not running the HVAC during off hours,

building pressurization gets thrown out of whack and humidity may

build up. These are not the words that energy engineers would like

to hear! :)

Ian Cull, PE, CIE

Chelsea Training

www.invironment.com

www.LabComparisons.com

>

> Dear Ian:

>

> If the modification to the ASHRAE minimum recommended ventilation

rate to achieve " acceptable " IAQ now includes a term that is based

on square footage of the space being ventilated, I ask if the intent

of this change is to address the air contaminants off-gassing from

the furnishings, and since this off-gassing occurs on a 24/7 basis,

should the ventilation minimum recommendation be provided on a 24/7

basis as well?

>

> What I'm seeing is aggressive ventilation rates being provided

during peak occupancy, on the order of 24 cfm person of outdoor air

delivered. But thev limited hours of operation of this ventilation

provided in a tight building leaves a residual of bioeffluents, and

presumably air contaminants off-gassed during the overnight

interval, that persist until occupancy the next morning.

>

> In terms of good engineering practice, shouldn't a complete

flushout of the previous day's bioeffluents be achieved overnight,

so the building's air doesn't seem stale upon reentry by people the

next day?

>

> Does ASHRAE deal with this issue?

>

> Sincerely,

>

> W. Bearg, PE, CIH

> Building Scientist

> Concord, MA

>

> --

> Director of IAQ Programs

> AIRxpert Systems, Inc.

> www.AIRxpert.com

>

>

> -------------- Original message ----------------------

>

>

Link to comment
Share on other sites

Dear Ian:

Does ASHRAE maintain its definition of " acceptable " IAQ as the case where a

substantial majority (80% or more) of the people exposed do not express

dissatifaction. " This is what appears in the 1999 version.

I also wonder if a statement appears that indicates that increases above the

minimum recommended ventilation rate might be needed to reduce the nuimber of

dissatisfied people to below 20%.

Sincerely,

W. Bearg, PE, CIH

-------------- Original message ----------------------

,

My understanding is that the cfm/square foot in the new ASHRAE Std.

62.1-2004 is indeed to address the building's contribution to

unacceptable IAQ. This is a huge improvement on the previous

standard that only considers the human contribution.

You make a great point that I didn't consider. The human

contribution only happens when the space is occupied, and when it's

occupied, the outdoor air is being brought in. There may be

little/no ventilation to deal with the building's contribution at

night.

To my knowledge, ASHRAE doesn't address the night set back issue.

Just to be safe, I did a word search on " night " and " set back " on my

electronic copy of 62.1. Not a single word came up.

To add to the problems of not running the HVAC during off hours,

building pressurization gets thrown out of whack and humidity may

build up. These are not the words that energy engineers would like

to hear! :)

Ian Cull, PE, CIE

Chelsea Training

www.invironment.com

www.LabComparisons.com

>

> Dear Ian:

>

> If the modification to the ASHRAE minimum recommended ventilation

rate to achieve " acceptable " IAQ now includes a term that is based

on square footage of the space being ventilated, I ask if the intent

of this change is to address the air contaminants off-gassing from

the furnishings, and since this off-gassing occurs on a 24/7 basis,

should the ventilation minimum recommendation be provided on a 24/7

basis as well?

>

> What I'm seeing is aggressive ventilation rates being provided

during peak occupancy, on the order of 24 cfm person of outdoor air

delivered. But thev limited hours of operation of this ventilation

provided in a tight building leaves a residual of bioeffluents, and

presumably air contaminants off-gassed during the overnight

interval, that persist until occupancy the next morning.

>

> In terms of good engineering practice, shouldn't a complete

flushout of the previous day's bioeffluents be achieved overnight,

so the building's air doesn't seem stale upon reentry by people the

next day?

>

> Does ASHRAE deal with this issue?

>

> Sincerely,

>

> W. Bearg, PE, CIH

> Building Scientist

> Concord, MA

>

> --

> Director of IAQ Programs

> AIRxpert Systems, Inc.

> www.AIRxpert.com

>

>

> -------------- Original message ----------------------

>

>

Link to comment
Share on other sites

,

ASHRAE did keep their definition of acceptable indoor air quality.

Although a lot of attention gets focused on the 80% rule, the most

important word in the definition typically gets overlooked. I think

the most important word is the " and " in the middle of the

definition. The definition requires that the air be both healthy

and comfortable.

The 80% rule deals with the comfort end of things (odors, general

subjective " satisfaction " ). Their other half talks about

health... " air in which there are no known contaminants at harmful

concentrations as determined by cognizant authorities "

The 80% rule should be viewed in light of the rest of the

definition. Sure the definition has its problems, but it carries

the important concept of achieving both health and comfort.

For others out there, here is ASHRAE's definition of acceptable IAQ:

" acceptable indoor air quality: air in which there are no known

contaminants at harmful concentrations as determined by cognizant

authorities AND with which a substantial majority (80% or more) of

the people exposed do not express dissatisfaction. "

-from ASHRAE 62.1-2004 (emphasis on the " and " added by me)

, I don't see any mention of increasing ventilation beyond

minimums to increase satisfaction beyond 80%.

Ian Cull, PE, CIE

Chelsea Training

www.invironment.com

www.LabComparisons.com

----------------------------

Dear Ian:

Does ASHRAE maintain its definition of " acceptable " IAQ as the case

where a substantial majority (80% or more) of the people exposed do

not express dissatifaction. " This is what appears in the 1999

version.

I also wonder if a statement appears that indicates that increases

above the minimum recommended ventilation rate might be needed to

reduce the nuimber of dissatisfied people to below 20%.

Sincerely,

W. Bearg, PE, CIH

Link to comment
Share on other sites

Dear Ian:

Focusing on the words, " no known contaminants at harmful concentrations " ,

Several questions come to mind.

Firstly, is this just long-term harm, are does it include short-term harm, such

as caused by irritating air contaminants? How does ASHRAE define " harm " ?

Secondly, since people spew air contaminants (i.e., bioeffluents) that can be

contagious in nature (colds and flu), do you suggest sampling to document that

there are none of these germs present?

If increased ventilation rates, above the ASHRAE minimum recommended minimum

rates, have been shown to reduce short-term absenteeism (1), presumably by

reducing exposures to contagious airborne contaminants, shouldn't the goal of

providing a healthy indoor environment make note of this?

Just some thoughts.

Sincerely,

W. Bearg, PE, CIH

Concord, MA

Footnote (1): Milton, et.al. Risk of Sick Leave Associated with Outdoor Air

Supply Rate, Humidification, and Occupant Complaints. Indoor Air 2000; 10:

212-221

-------------- Original message ----------------------

,

ASHRAE did keep their definition of acceptable indoor air quality.

Although a lot of attention gets focused on the 80% rule, the most

important word in the definition typically gets overlooked. I think

the most important word is the " and " in the middle of the

definition. The definition requires that the air be both healthy

and comfortable.

The 80% rule deals with the comfort end of things (odors, general

subjective " satisfaction " ). Their other half talks about

health... " air in which there are no known contaminants at harmful

concentrations as determined by cognizant authorities "

The 80% rule should be viewed in light of the rest of the

definition. Sure the definition has its problems, but it carries

the important concept of achieving both health and comfort.

For others out there, here is ASHRAE's definition of acceptable IAQ:

" acceptable indoor air quality: air in which there are no known

contaminants at harmful concentrations as determined by cognizant

authorities AND with which a substantial majority (80% or more) of

the people exposed do not express dissatisfaction. "

-from ASHRAE 62.1-2004 (emphasis on the " and " added by me)

, I don't see any mention of increasing ventilation beyond

minimums to increase satisfaction beyond 80%.

Ian Cull, PE, CIE

Chelsea Training

www.invironment.com

www.LabComparisons.com

----------------------------

Dear Ian:

Does ASHRAE maintain its definition of " acceptable " IAQ as the case

where a substantial majority (80% or more) of the people exposed do

not express dissatifaction. " This is what appears in the 1999

version.

I also wonder if a statement appears that indicates that increases

above the minimum recommended ventilation rate might be needed to

reduce the nuimber of dissatisfied people to below 20%.

Sincerely,

W. Bearg, PE, CIH

Link to comment
Share on other sites

,

You ask some great questions. How does ASHRAE define " harm " ? Well

they pass the buck to " cognizant authorities " like ACGIH, OSHA,

NIOSH and others with exposure limits. That opens up a whole can of

worms because these are for occupational settings with healthy adult-

aged workers. What about the immunocompromised, allergic and

chemically sensitive out there?

I like the definition of health from the World Health Organization

(who? WHO) that hasn't changed since it came out in 1948:

" Health is a state of complete physical, mental and social well

being and not merely the absence of disease or infirmity. "

I find that it's a huge task to label a space as having acceptable

IAQ. Unless you test the air as you suggested, there is no way of

knowing.

Ian Cull, PE, CIE

Chelsea Training

www.invironment.com

www.LabComparisons.com

>

> Dear Ian:

>

> Focusing on the words, " no known contaminants at harmful

concentrations " ,

>

> Several questions come to mind.

>

> Firstly, is this just long-term harm, are does it include short-

term harm, such as caused by irritating air contaminants? How does

ASHRAE define " harm " ?

>

> Secondly, since people spew air contaminants (i.e., bioeffluents)

that can be contagious in nature (colds and flu), do you suggest

sampling to document that there are none of these germs present?

>

> If increased ventilation rates, above the ASHRAE minimum

recommended minimum rates, have been shown to reduce short-term

absenteeism (1), presumably by reducing exposures to contagious

airborne contaminants, shouldn't the goal of providing a healthy

indoor environment make note of this?

>

> Just some thoughts.

>

>

> Sincerely,

>

> W. Bearg, PE, CIH

> Concord, MA

>

> Footnote (1): Milton, et.al. Risk of Sick Leave Associated with

Outdoor Air Supply Rate, Humidification, and Occupant Complaints.

Indoor Air 2000; 10: 212-221

>

>

> -------------- Original message ----------------------

>

>

Link to comment
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...