Guest guest Posted December 26, 2006 Report Share Posted December 26, 2006 Dear Ravi, Please refer OISD 118 point no 7.0 for dyke capaciy and minimum height requirements. M.Balachandran. ravi safety Sent by: indiansafetyprofessionals 26/12/06 05:19 PM To indiansafetyprofessionals cc Subject Dyke wall height Dear all Normally dyke wall are constructed to hold 120% of the capcity of largest tank. I want know what is minimum height of the wall. Also request you send related standards regards ravi Send free SMS to your Friends on Mobile from your Yahoo! Messenger. Download Now! http://messenger.yahoo.com/download.php Disclaimer : Information contained and transmitted by this E-MAIL is proprietary to TotalFinaElf India Limited and is intended for use only by the individual or entity to which it is addressed, and may contain information that is privileged, confidential or exempt from disclosure under applicable law. If this is a forwarded message, the content of this E-MAIL may not have been sent with the authority of the Company. If you are not the intended recipient, an agent of the intended recipient or a person responsible for delivering the information to the named recipient, you are notified that any use, distribution, transmission, printing, copying or dissemination of this information in any way or in any manner is strictly prohibited. If you have received this communication in error, please delete this mail & notify us immediately at notes@... Quote Link to comment Share on other sites More sharing options...
Guest guest Posted December 26, 2006 Report Share Posted December 26, 2006 Dear Ravi, The general rule for Dyke is it should take normally 110% volume of the tank. Example if u r storing 100liters of water the dyke should have the capacity to hold 110 liters of water. With Regards Dinesh Re: Dyke wall height Dear Ravi, Please refer OISD 118 point no 7.0 for dyke capaciy and minimum height requirements. M.Balachandran. This e-mail message may contain privileged and/or confidential information, and is intended to be received only by persons entitled to receive such information. If you have received this e-mail in error, please notify the sender immediately. Please delete it and all attachments from any servers, hard drives or any other media. Other use of this e-mail by you is strictly prohibited. All e-mails and attachments sent and received are subject to monitoring, reading and archival by Monsanto. The recipient of this e-mail is solely responsible for checking for the presence of "Viruses" or other "Malware". Monsanto accepts no liability for any damage caused by any such code transmitted by or accompanying this e-mail or any attachment. Quote Link to comment Share on other sites More sharing options...
Guest guest Posted December 26, 2006 Report Share Posted December 26, 2006 Dear Dinesh, A fine tuned version, " It should be 110 % of of the largest tank after deducting hold up area of that particular tank " . Regards. M.Balachandran. " M, DINESH [AG/8016] " 27/12/06 11:50 AM To , " ravi safety " cc <indiansafetyprofessionals > Subject RE: Dyke wall height Dear Ravi, The general rule for Dyke is it should take normally 110% volume of the tank. Example if u r storing 100liters of water the dyke should have the capacity to hold 110 liters of water. With Regards Dinesh Re: Dyke wall height Dear Ravi, Please refer OISD 118 point no 7.0 for dyke capaciy and minimum height requirements. M.Balachandran. This e-mail message may contain privileged and/or confidential information, and is intended to be received only by persons entitled to receive such information. If you have received this e-mail in error, please notify the sender immediately. Please delete it and all attachments from any servers, hard drives or any other media. Other use of this e-mail by you is strictly prohibited. All e-mails and attachments sent and received are subject to monitoring, reading and archival by Monsanto. The recipient of this e-mail is solely responsible for checking for the presence of " Viruses " or other " Malware " . Monsanto accepts no liability for any damage caused by any such code transmitted by or accompanying this e-mail or any attachment. Disclaimer : Information contained and transmitted by this E-MAIL is proprietary to TotalFinaElf India Limited and is intended for use only by the individual or entity to which it is addressed, and may contain information that is privileged, confidential or exempt from disclosure under applicable law. If this is a forwarded message, the content of this E-MAIL may not have been sent with the authority of the Company. If you are not the intended recipient, an agent of the intended recipient or a person responsible for delivering the information to the named recipient, you are notified that any use, distribution, transmission, printing, copying or dissemination of this information in any way or in any manner is strictly prohibited. If you have received this communication in error, please delete this mail & notify us immediately at notes@... Quote Link to comment Share on other sites More sharing options...
Guest guest Posted December 27, 2006 Report Share Posted December 27, 2006 Dear Sir, Since gone through the three-four mails & all are giving about the largest tank capacity volume will be the dyke wall capacity, but the question arises what is the capacity of the dykewall if there are 3 tanks of same capacity & if there is an potential of getting bursting of all three tanks?? The maximum dyke wall height is 1.2 m Regards Nilesh A Bhayani Safety Officer Indian Rayon. From: indiansafetyprofessionals Sent: Wednesday, December 27, 2006 12:54 PM To: balachandran.m@...; ravi safety Cc: indiansafetyprofessionals Subject: RE: Dyke wall height Dear Ravi, The general rule for Dyke is it should take normally 110% volume of the tank. Example if u r storing 100liters of water the dyke should have the capacity to hold 110 liters of water. With Regards Dinesh -----Original Message----- From: indiansafetyprofessionals [mailto:indiansafetyprofessionals ] On Behalf Of balachandran.m@...elf.co.in Sent: Wednesday, December 27, 2006 10:09 AM To: ravi safety Cc: indiansafetyprofessionals Subject: Re: Dyke wall height Dear Ravi, Please refer OISD 118 point no 7.0 for dyke capaciy and minimum height requirements. M.Balachandran. This e-mail message may contain privileged and/or confidential information, and is intended to be received only by persons entitled to receive such information. If you have received this e-mail in error, please notify the sender immediately. Please delete it and all attachments from any servers, hard drives or any other media. Other use of this e-mail by you is strictly prohibited. All e-mails and attachments sent and received are subject to monitoring, reading and archival by Monsanto. The recipient of this e-mail is solely responsible for checking for the presence of " Viruses " or other " Malware " . Monsanto accepts no liability for any damage caused by any such code transmitted by or accompanying this e-mail or any attachment. Quote Link to comment Share on other sites More sharing options...
Guest guest Posted December 27, 2006 Report Share Posted December 27, 2006 Dear All, Generally and even in HAZOP study multiple failures are not considered to establish " Operation Control - Engineering " . Please consider one of the largest capacity of tank (though you have more of same size) for dyke wall construction . System to take of multiple failure may be " Emergency or Disaster Management Plan " Please validate my statement through some renowned consultants or statutory authority before taking it granted. My understanding may not fully right. Regards. M.Balachandran. " Safety Deptt. " Sent by: indiansafetyprofessionals 27/12/06 02:22 PM To " M, DINESH [AG/8016] " cc indiansafetyprofessionals Subject RE: Dyke wall height Dear Sir, Since gone through the three-four mails & all are giving about the largest tank capacity volume will be the dyke wall capacity, but the question arises what is the capacity of the dykewall if there are 3 tanks of same capacity & if there is an potential of getting bursting of all three tanks?? The maximum dyke wall height is 1.2 m Regards Nilesh A Bhayani Safety Officer Indian Rayon. From: indiansafetyprofessionals Sent: Wednesday, December 27, 2006 12:54 PM To: balachandran.m@...; ravi safety Cc: indiansafetyprofessionals Subject: RE: Dyke wall height Dear Ravi, The general rule for Dyke is it should take normally 110% volume of the tank. Example if u r storing 100liters of water the dyke should have the capacity to hold 110 liters of water. With Regards Dinesh Re: Dyke wall height Dear Ravi, Please refer OISD 118 point no 7.0 for dyke capaciy and minimum height requirements. M.Balachandran. This e-mail message may contain privileged and/or confidential information, and is intended to be received only by persons entitled to receive such information. If you have received this e-mail in error, please notify the sender immediately. Please delete it and all attachments from any servers, hard drives or any other media. Other use of this e-mail by you is strictly prohibited. All e-mails and attachments sent and received are subject to monitoring, reading and archival by Monsanto. The recipient of this e-mail is solely responsible for checking for the presence of " Viruses " or other " Malware " . Monsanto accepts no liability for any damage caused by any such code transmitted by or accompanying this e-mail or any attachment. Disclaimer : Information contained and transmitted by this E-MAIL is proprietary to TotalFinaElf India Limited and is intended for use only by the individual or entity to which it is addressed, and may contain information that is privileged, confidential or exempt from disclosure under applicable law. If this is a forwarded message, the content of this E-MAIL may not have been sent with the authority of the Company. If you are not the intended recipient, an agent of the intended recipient or a person responsible for delivering the information to the named recipient, you are notified that any use, distribution, transmission, printing, copying or dissemination of this information in any way or in any manner is strictly prohibited. If you have received this communication in error, please delete this mail & notify us immediately at notes@... Quote Link to comment Share on other sites More sharing options...
Guest guest Posted December 27, 2006 Report Share Posted December 27, 2006 Gentlemen, When you work out the probability of a failure of a tank.............it would be a very minimum. Because it has its own design features, factor of safety etc.... which will ensure that the failure probability is very minimum. Many a times it will be in fractions ( ie less than 1) When you consider the probability of all tanks failure at a given time, the probability will be very very less........................... ( Because the probability all tanks failure at a given time would be.................... Probability of tank 1 X probability 2 X Prabobality of tank3...................which would be very very less...............For eg...If you multiply a fraction with another fraction you get much lesser value ....................0.5X0.5=0.25) You can see the probability of two tanks at a time is reduced.....When more tanks are there, the probability still gets reduced.....more & more as the multiplication with fraction increases) Hence it would be more appropriate to plan for a high probability event ie the probability of failure of the biggest tank in a cluster of tanks. Hence the secondary containment for the biggest tank would be a technoeconomical consideration. However a word of caution.......................................The tanks should have minimum distance maintained in between them as per the relevant standards . regards Balaji SCHLUMBERGER At 15:41 27-12-06, balachandran.m@... wrote: Dear All, Generally and even in HAZOP study multiple failures are not considered to establish " Operation Control - Engineering " . Please consider one of the largest capacity of tank (though you have more of same size) for dyke wall construction . System to take of multiple failure may be " Emergency or Disaster Management Plan " Please validate my statement through some renowned consultants or statutory authority before taking it granted. My understanding may not fully right. Regards. M.Balachandran. " Safety Deptt. " Sent by: indiansafetyprofessionals 27/12/06 02:22 PM To " M, DINESH [AG/8016] " cc indiansafetyprofessionals Subject RE: Dyke wall height Dear Sir, Since gone through the three-four mails & all are giving about the largest tank capacity volume will be the dyke wall capacity, but the question arises what is the capacity of the dykewall if there are 3 tanks of same capacity & if there is an potential of getting bursting of all three tanks?? The maximum dyke wall height is 1.2 m Regards Nilesh A Bhayani Safety Officer Indian Rayon. From: indiansafetyprofessionals [ mailto:dinesh.m@...] Sent: Wednesday, December 27, 2006 12:54 PM To: balachandran.m@...; ravi safety Cc: indiansafetyprofessionals Subject: RE: Dyke wall height Dear Ravi, The general rule for Dyke is it should take normally 110% volume of the tank. Example if u r storing 100liters of water the dyke should have the capacity to hold 110 liters of water. With Regards Dinesh Re: Dyke wall height Dear Ravi, Please refer OISD 118 point no 7.0 for dyke capaciy and minimum height requirements. M.Balachandran. This e-mail message may contain privileged and/or confidential information, and is intended to be received only by persons entitled to receive such information. If you have received this e-mail in error, please notify the sender immediately. Please delete it and all attachments from any servers, hard drives or any other media. Other use of this e-mail by you is strictly prohibited. All e-mails and attachments sent and received are subject to monitoring, reading and archival by Monsanto. The recipient of this e-mail is solely responsible for checking for the presence of " Viruses " or other " Malware " . Monsanto accepts no liability for any damage caused by any such code transmitted by or accompanying this e-mail or any attachment. Disclaimer : Information contained and transmitted by this E-MAIL is proprietary to TotalFinaElf India Limited and is intended for use only by the individual or entity to which it is addressed, and may contain information that is privileged, confidential or exempt from disclosure under applicable law. If this is a forwarded message, the content of this E-MAIL may not have been sent with the authority of the Company. If you are not the intended recipient, an agent of the intended recipient or a person responsible for delivering the information to the named recipient, you are notified that any use, distribution, transmission, printing, copying or dissemination of this information in any way or in any manner is strictly prohibited. If you have received this communication in error, please delete this mail & notify us immediately at notes@... Quote Link to comment Share on other sites More sharing options...
Guest guest Posted January 1, 2007 Report Share Posted January 1, 2007 Mr Balaji's statement on dyke wall is correct with further fine tuning Normally 110% of largest tank is considered adequate with all other precautions as stated by Mr Balaji Further the volatility rate, cryogenic conditions are also to be considered whether it is superheated/subcooled or not etc and allowance to be given accordingly. Balaji Muthukrishnan Balaji Muthukrishnan Sent by: indiansafetyprofessionals 27/12/2006 04:38 PM To balachandran.m@..., " Safety Deptt. " cc " M, DINESH [AG/8016] " , indiansafetyprofessionals Subject RE: Dyke wall height Gentlemen, When you work out the probability of a failure of a tank.............it would be a very minimum. Because it has its own design features, factor of safety etc.... which will ensure that the failure probability is very minimum. Many a times it will be in fractions ( ie less than 1) When you consider the probability of all tanks failure at a given time, the probability will be very very less........................... ( Because the probability all tanks failure at a given time would be.................... Probability of tank 1 X probability 2 X Prabobality of tank3...................which would be very very less...............For eg...If you multiply a fraction with another fraction you get much lesser value ...................0.5X0.5=0.25) You can see the probability of two tanks at a time is reduced.....When more tanks are there, the probability still gets reduced.....more & more as the multiplication with fraction increases) Hence it would be more appropriate to plan for a high probability event ie the probability of failure of the biggest tank in a cluster of tanks. Hence the secondary containment for the biggest tank would be a technoeconomical consideration. However a word of caution.......................................The tanks should have minimum distance maintained in between them as per the relevant standards . regards Balaji SCHLUMBERGER At 15:41 27-12-06, balachandran.m@... wrote: Dear All, Generally and even in HAZOP study multiple failures are not considered to establish " Operation Control - Engineering " . Please consider one of the largest capacity of tank (though you have more of same size) for dyke wall construction . System to take of multiple failure may be " Emergency or Disaster Management Plan " Please validate my statement through some renowned consultants or statutory authority before taking it granted. My understanding may not fully right. Regards. M.Balachandran. " Safety Deptt. " Sent by: indiansafetyprofessionals 27/12/06 02:22 PM To " M, DINESH [AG/8016] " cc indiansafetyprofessionals Subject RE: Dyke wall height Dear Sir, Since gone through the three-four mails & all are giving about the largest tank capacity volume will be the dyke wall capacity, but the question arises what is the capacity of the dykewall if there are 3 tanks of same capacity & if there is an potential of getting bursting of all three tanks?? The maximum dyke wall height is 1.2 m Regards Nilesh A Bhayani Safety Officer Indian Rayon. From: indiansafetyprofessionals [ mailto:dinesh.m@...] Sent: Wednesday, December 27, 2006 12:54 PM To: balachandran.m@...; ravi safety Cc: indiansafetyprofessionals Subject: RE: Dyke wall height Dear Ravi, The general rule for Dyke is it should take normally 110% volume of the tank. Example if u r storing 100liters of water the dyke should have the capacity to hold 110 liters of water. With Regards Dinesh Re: Dyke wall height Dear Ravi, Please refer OISD 118 point no 7.0 for dyke capaciy and minimum height requirements. M.Balachandran. This e-mail message may contain privileged and/or confidential information, and is intended to be received only by persons entitled to receive such information. If you have received this e-mail in error, please notify the sender immediately. Please delete it and all attachments from any servers, hard drives or any other media. Other use of this e-mail by you is strictly prohibited. All e-mails and attachments sent and received are subject to monitoring, reading and archival by Monsanto. The recipient of this e-mail is solely responsible for checking for the presence of " Viruses " or other " Malware " . Monsanto accepts no liability for any damage caused by any such code transmitted by or accompanying this e-mail or any attachment. Disclaimer : Information contained and transmitted by this E-MAIL is proprietary to TotalFinaElf India Limited and is intended for use only by the individual or entity to which it is addressed, and may contain information that is privileged, confidential or exempt from disclosure under applicable law. If this is a forwarded message, the content of this E-MAIL may not have been sent with the authority of the Company. If you are not the intended recipient, an agent of the intended recipient or a person responsible for delivering the information to the named recipient, you are notified that any use, distribution, transmission, printing, copying or dissemination of this information in any way or in any manner is strictly prohibited. If you have received this communication in error, please delete this mail & notify us immediately at notes@... **********Please visit us at www.itcportal.com********** ****************************************************************************** This Communication is for the exclusive use of the intended recipient (s) and shall not attach any liability on the originator or ITC Ltd./its Subsidiaries/its Group Companies. If you are the addressee, the contents of this email are intended for your use only and it shall not be forwarded to any third party, without first obtaining written authorisation from the originator or ITC Ltd./its Subsidiaries/its Group Companies. It may contain information which is confidential and legally privileged and the same shall not be used or dealt with by any third party in any manner whatsoever without the specific consent of ITC Ltd./its Subsidiaries/its Group Companies. ******************************************************************************** Quote Link to comment Share on other sites More sharing options...