Hydraulic testing of pressure vessels is required under IS 2190,which is the maintenance code for fire extinguishers.

As per the code ,the hydrotest is required to be conducted for :

Co2/any stored pressure type fire extgrs. - Each time when refilled/If not refilled then once in 5yrs.

DCP- Once in three years.

Water Type- Once in two years.

Regards

Arvind Bodhankar

{Disarmed} Re: {Disarmed} Hydraulic testing of fire extinguishers

Dear all,

Hyd.testing of vessels is required where we store gas/liquid at certain specified pressure.In case of fire extinguishers, question of holding pressure does not arise.

I think that is the reason BIS does not specify hyd. testing in this case.

Regards,

M L Dahima

{Disarmed} Hydraulic testing of fire extinguishers

Dear EHS Professionals,

We do mostly come across the issue of fire ext, hydraulic testing because it is a pressurised vessels.

I am not aware as the testing is required or not? if it is required then under what statute?

BIS does specify for maintenance but not for hydraulic testing.

Will we share views on it.

Thanks and regards

SKP Srivastva

Trident Group of Companies,

Barnala, Punjab.

098159 99711

Find out what India is talking about on - Yahoo! Answers India Send FREE SMS to your friend's mobile from Yahoo! Messenger Version 8. Get it NOW

The information contained in this communication and its attachment(s) is intended only for the use of the individual to whom it is addressed and may contain information that is privileged, confidential, or exempt from disclosure. If the reader of this message is not the intended recipient, you are hereby notified that any dissemination, distribution, or copying of this communication is strictly prohibited. If you have received this communication in error, please notify postmaster@... and delete the communication without retaining any copies. Thank you. Translations available: http://www.owenscorning.com/emailfooter.html

Link to comment
Share on other sites

Dear all,

Hyd.testing of vessels is required where we store gas/liquid at certain specified pressure.In case of fire extinguishers, question of holding pressure does not arise.

I think that is the reason BIS does not specify hyd. testing in this case.

Regards,

M L Dahima

{Disarmed} Hydraulic testing of fire extinguishers

Dear EHS Professionals,

We do mostly come across the issue of fire ext, hydraulic testing because it is a pressurised vessels.

I am not aware as the testing is required or not? if it is required then under what statute?

BIS does specify for maintenance but not for hydraulic testing.

Will we share views on it.

Thanks and regards

SKP Srivastva

Trident Group of Companies,

Barnala, Punjab.

098159 99711

Find out what India is talking about on - Yahoo! Answers India Send FREE SMS to your friend's mobile from Yahoo! Messenger Version 8. Get it NOW

Link to comment
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...