Hi ,

If the

conference room HVAC was appropriately designed, then thermal comfort and appropriate

ventilation rates should be achievable without fully opening the VAV.

If the design

temperature in the room is achieved, then the VAV box will and should back-off.

Also the VAV

may also be set-up so that it does not fully open under any circumstances (except

possibly smoke purge).

Many design

deficiencies are associated with the tenancy fitout designs. Remember that more

than likely the base building was designed (in the 1980’s~mid 2000 era) for

open plan, unpartitioned space and then the occupant was supposed to engage a

competent designer to ensure that the HVAC was amended to reflect their

specific occupancy.

Cost

constraints usually meant that this was achieved using the base building HVAC

and we know just how ineffective that this is for conference rooms etc and

especially where base building VAV systems are used.

I recently

reviewed a system where the conference room was supplied by four (4) VAV’s with

the controlling thermostats all grouped together adjacent to the entry door.

The VAV’s were constantly hunting for setpoint and this was further compromised

by the customer installing slab-to-slab partitioning (for acoustic seal and for

security) which was obstructing the return air through the ceiling plenum.

Conference

rooms are by their very nature a transient load with variant occupation numbers

and to achieve thermal comfort as well as adequate diffusion rates requires a

quite sophisticated design. I would always lean toward something with a broad

range of capacity control for the room and would base it at not less than the

maximum expected occupation within any 30-minute period (usually seating

capacity +10% at 300W/seat + fabric load) and diffusion ventilation capacity rates

of not less than 10L/s/person of Outside Air where high grade filtration is

used increasing to 30L/s/person for medium grade filtration.

Temperature Control

should be by thermostat while OA ventilation supply to the room should be by

CO2 sensing.

Unless VAV’s

are exclusively responding to fabric/solar loads, they should be controlled by

a single zone thermostat.

Return air

capacity from the room should be verified.

Regards,

Engineering & Compliance Support for Building

Services

 

Ian

Childs

New Directions

International Business Services Pty Limited

ABN.49.083.184.751

PO Box 26 Oatley NSW 2223 Australia

ian@...

www.ndibs.com.au

www.safeworkmethod.com.au

www.oatleyweather.com.au

MSN: childsian@...

YM: newdirectionsint

ICQ: 85002610

AIM: ianatndibs

telephone:

fax Sydney:

fax Melbourne:

fax Brisbane:

mobile:

VoIP Skype ID:

VoIP softphone:

+61(0)2 9594

4477

+61(0)2

8090 1026

+61(0)2 8569 1015

+61(0)3 8080 1795

+61(0)7 3319 8999

+61(0)414 472 042

childsian

09141426mynetfone.au

Building Services

Engineering & Facility Maintenance Management Advisory, Fire Safety

Reports & Statements, OH & S, Forensic Engineering, IR‑Thermography, Energy Audits, Environmental Audits, 

Building Code Assessments, Disability Access, Risk Evaluation,

Material Hazard, Water‑Quality, Air Quality, Thermal Comfort &

Close Control A/C, Smoke Control, Equipment condition assessments

Add me to your address book...

more info?

DISCLAIMER AND TERMS

GOVERNING ELECTRONIC COMMUNICATIONS

This e-mail (including any attachments) is confidential and may

be protected by legal professional privilege. If you are not the intended

recipient of this e-mail you are advised that any use, reproduction,

disclosure or distribution of the information contained in the e-mail is

prohibited. If you have received this e-mail in error please reply to us

immediately and delete the e-mail. While an up to date anti-virus software

is being used by us, no warranty is made that this e-mail is free from

computer virus or other defect. Any loss/damage incurred by using this

e-mail is not the sender’s responsibility.

Please consider  not printing

this email unless absolutely necessary

__________ Information from ESET NOD32 Antivirus, version of virus signature database 4733 (20091231) __________The message was checked by ESET NOD32 Antivirus.http://www.eset.com

Link to comment
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...