Guest guest Posted April 7, 2006 Report Share Posted April 7, 2006 , I posted this when the study came out: In a recent paper, “Effect of ultraviolet germicidal lights in office ventilation systems on workers’ health and well-being: double-blind multiple crossover trial,” (Lancet 2003; 362: 1785-91), the authors Menzies et.al. concluded that “installation of UVGI in most North American offices could resolve work-related symptoms in about 4 million employees, caused by microbial contamination of the heating, ventilation and air-conditioning systems.” Despite the fact that ultraviolet germicidal irradiation (UVGI) has been shown in many previous studies to reduce airborne contagion, I believe that the conclusion of this study overstates the impact of UVGI on HVAC systems and office indoor air quality. Three healthy, well-ventilated (peak values of carbon dioxide were under 620 ppm) office buildings in Montreal, Canada were evaluated over the course of one year (July 1999 to July 2000). In the study, UV lamps (245-266 nm wavelength band), rated at 450 mW/cm2 at a distance of one meter, were mounted with reflectors 15 to 74 cm from the cooling coils and drip pans. At this level of irradiation (greater than what is typical), the authors estimated that the survival time for resistant organisms would be less than 4 minutes. Within the HVAC system, the UVGI lamps were cycled, operating for 12 weeks off, and then 4 consecutive weeks on. Questionnaires were repeatedly distributed to about 800 office workers to obtain subjective opinions regarding environmental satisfaction and allergy symptoms (categories included systemic, mucosal, respiratory, musculo-skeletal, and “any symptom”) during the different time intervals. The concentration of microbes on the coils and in the drip pans was determined by placing sterile 5 cm x 5 cm “coupons” of sheet metal on the surfaces (exposed directly to the UVGI), and then placing the exposed coupons on a Petri dish containing culture media (Sabouraud or MEA), and incubating the dishes. Coupons (receiving no UVGI) were also placed on the filters. Air samples indoors and outdoors were obtained with Burkard volumetric air samplers (with Petri dishes) to determine the concentration of fungal spores. A total of 1240 samples were assayed. Endotoxin concentrations were determined using volumetric sampling and polycarbonate filter cassettes for the air, and by washings directly from the dust impacted on the coupon surfaces. A total of 284 samples were assayed. Airborne endotoxin was not detectable at workstations with the UVGI either on or off and there was a slight increase in levels on the filter coupons with the UVGI on. The amount of endotoxin on the coil coupon dropped from 8 endotoxin units (EU) to zero with the UVGI on. Culturable air samples for fungal spores at both the returns and supplies, with the UVGI both on and off, were 0 (zero) cfu/m3. The number of culturable spores per 25 cm2 on all coupons was very low, and averaged at the cooling coil from 0 (UVGI on) to about 4 (UVGI off) or far less than one spore per cm2 after a 4- or 12-week exposure period. The coupons on the filters collected 3 cfu/coupon (UVGI off) and 2 cfu/coupon (UVGI on). The coupons may not have been very efficient collectors since they lacked a “sticky” coating and were positioned perpendicular to the air flows and thus obstructed the stream lines. In addition, the irradiated coupons were exposed directly to the UVGI, whereas microbes on an actual HVAC surface would have received incident light at a variety of angles, the intensity of which would be attenuated by the dust accumulations. The data and results for different seasons were not separated. Since in Montreal there is a long heating season and a short cooling season, the expected results for each season should be quite different. In addition, during the heating season there is no condensation of moisture to promote microbial growth. In fact, in the presence of minimal dust on the coupons and few organisms, and without moisture, there is little opportunity for any microbial amplification, either in the heating or cooling season. Despite the reported reduction in symptoms indoors at work during the UVGI-on periods, no statistically significant differences were reported in the indoor air concentrations of microbes at work stations; thus the authors were left with no explanation for the reported reduction in symptoms associated with UVGI. (The authors postulated that the UVGI radiation may have somehow reduced the aerosolization of microbial antigenic proteins.) To prevent microbial growth due to moisture or high relative humidity in HVAC systems, the most important components of hygiene will always be proper design to begin with, adequate filtration (a minimum of MERV 6-8), and regular maintenance. Though UVGI may certainly serve as an adjunct in disinfecting exposed air and reducing microbial growth on irradiated surfaces, the impact on overall indoor air quality of UVGI alone should not be overstated. C. May May Indoor Air Investigations LLC 1522 Cambridge Street Cambridge, MA 02139 www.mayindoorair.com www.myhouseiskillingme.com iamnotanairhead writes: > Hi all, > > Not too long ago, AirwaysEnv@... wrote: > >>Unfortunately, science and scientists do not exist outside of >> economics and finance. It can be seen in the way new technologies >>are marketed today that the line between science and marketing gets >> fuzzier and fuzzier. How about all these pharmaceutical >> advertisements on television today? Or ozone generating air >> purifiers. Or the science behind UV light bulbs in ducts to kill >>mold spores whizzing by... > > I thought that the science behind germicidal UV was sound. Anyone have > any thoughts on the matter? > > Thanks, > Quote Link to comment Share on other sites More sharing options...
Guest guest Posted April 7, 2006 Report Share Posted April 7, 2006 , You have to read the words several times to catch the drift of what is being said. I support your belief in the efficacy of germicidal UV. To prove the concept just do a web search of <UV hospital McGill> What you were reading was a slam at the misuse of good science by inexperienced engineer types who claim germicidal UV will kill all the bad bugs. It doesn't! It only can kill what passes close enough to its killing field to be fatally irradiated. It does however do wonders for the HVAC trade when it installed close enough before the cooling coils to inhibit normal mold growth that robs a cooling system of its efficiency. But as far as killing the germs that make people sick there is a good bit of engineering needed before a germicidal UV system can be deemed reliable. However recent science has greatly enhanced the efficiency of UV bulbs for germicidal use by providing a target of titanium oxide so air passing by will literally be transformed into a fume of hydro peroxide and hydroxyl radicals which quickly attach themselves to bacteria, viruses and mold spores in such a way to defeat the cell wall so the cells either dies or loses the ability to reproduce. The process can be easily reviewed by doing a web search using various combinations of the following keywords: photocatalytic, photocatalysis, hospital, bacteria. You'll find many good scientific hits along with a few pushy promotions. Be well. Gibala ===================================== efficacy of germicidal UV Hi all,Not too long ago, AirwaysEnv@... wrote:>Unfortunately, science and scientists do not exist outside of > economics and finance. It can be seen in the way new technologies >are marketed today that the line between science and marketing gets > fuzzier and fuzzier. How about all these pharmaceutical > advertisements on television today? Or ozone generating air > purifiers. Or the science behind UV light bulbs in ducts to kill >mold spores whizzing by...I thought that the science behind germicidal UV was sound. Anyone have any thoughts on the matter?Thanks, Quote Link to comment Share on other sites More sharing options...
Guest guest Posted April 8, 2006 Report Share Posted April 8, 2006 : I, for one, believe the science behind UV irradiation as a germicidal method is very sound. I have seen (by my measurements) a tremendous reduction in active colony forming units inside HVAC systems (e.g., duct work, heat exchangers, fan blades, etc.) when UV lamps are installed. There was one negative comment recently about " UV killing spores whizzing by. " I for one believe it does work, although, like any engineering control, there are limitations. If the air speed (velocity) is really high and the UV lamp energy is low, there is a significant reduction in effect. If poorly designed/installed, the benefits of UV irradiation can be negligible. The lamps I have installed in HVAC systems are REALLY strong and warrant LOTO controls so they are not energized when the HVAC system is worked on, or if filters are changed. Moreover, they are shielded on the upstream side so debris/particulates do not impact and soil the bulbs. I usually place the lamps 4 to 6 inches from the heat exchanger (HE) on the upwind side, and rarely am I installing less than three lamps. I don't like placing them in dirty HVAC systems and when I install them on a retrofit, it is after the system is thoroughly cleaned. In side by side comparisons, i.e., HEs with lamps versus HEs without lamps, the cleanliness of the HEs with lamps could be easily seen one year later. In fact, the HEs (with lamps) looked as clean as the day the lamps were installed, while the other HEs had visible dirt on them. There is a lot to designing and installing UV systems in HVAC systems to make them effective - it is NOT a plug-n-play control. I know Kaiser Permanente has invested heavily in UV irradiation of their HVAC systems in an effort to control infection. I believe their results are really supportive of UV irradiation. A big advantage of UV irradiation is the low cost to operate. A big disadvantage is the high cost of each (good quality) bulb, and several bulbs are needed in each fan unit on small package units. On buildings with a centralized HVAC system (versus individual roof-mounted package units) there could be 20 to 30 bulbs, or more. Moreover, the HVAC fan unit must be so located that is can be easily serviced (not a problem with centralized HVAC systems). This is not the case in most residential construction because most architects/contractors design and place the fan unit in the attic...a very convenient but really dumb place to put a piece of machinery that needs periodic service with filters that warrant frequent replacing. If I had a house that had central air (I don't, we open windows) I would install UV irradiation along with an appropriate, well-sealed, HPFF filter bank; and it would deliver the cleanest air at the best, and lowest, operating cost. I am a believer in UV. For what it is worth... -- Geyer, PE, CIH, CSP President KENTEC Industries, Inc. Bakersfield, California www.kerntecindustries.com > Hi all, > > Not too long ago, AirwaysEnv@... wrote: > >> Unfortunately, science and scientists do not exist outside of >> economics and finance. It can be seen in the way new technologies >> are marketed today that the line between science and marketing gets >> fuzzier and fuzzier. How about all these pharmaceutical >> advertisements on television today? Or ozone generating air >> purifiers. Or the science behind UV light bulbs in ducts to kill >> mold spores whizzing by... > > I thought that the science behind germicidal UV was sound. Anyone have > any thoughts on the matter? > > Thanks, > > > > > > > > > > > FAIR USE NOTICE: > > This site contains copyrighted material the use of which has not always been > specifically authorized by the copyright owner. We are making such material > available in our efforts to advance understanding of environmental, political, > human rights, economic, democracy, scientific, and social justice issues, etc. > We believe this constitutes a 'fair use' of any such copyrighted material as > provided for in section 107 of the US Copyright Law. In accordance with Title > 17 U.S.C. Section 107, the material on this site is distributed without profit > to those who have expressed a prior interest in receiving the included > information for research and educational purposes. For more information go to: > http://www.law.cornell.edu/uscode/17/107.shtml. If you wish to use copyrighted > material from this site for purposes of your own that go beyond 'fair use', > you must obtain permission from the copyright owner. > Quote Link to comment Share on other sites More sharing options...
Guest guest Posted April 9, 2006 Report Share Posted April 9, 2006 Mike, I am not arguing that UV isn't germicidal, but without a clean system to begin with, and efficient filtration (minimum MERV 6-8, preferably MERV 11) in place to keep the linings and coil clean, UV is worthless. And few installers take the care that you seem to; based on the installations I've seen, most just pop a lamp in someplace and walk off with the exorbitant fee. For the money, I'd spend on cleaning and filtration before UV irradiation. C. May May Indoor Air Investigations LLC 1522 Cambridge Street Cambridge, MA 02139 www.mayindoorair.com www.myhouseiskillingme.com Geyer writes: > : > > I, for one, believe the science behind UV irradiation as a germicidal method > is very sound. I have seen (by my measurements) a tremendous reduction in > active colony forming units inside HVAC systems (e.g., duct work, heat > exchangers, fan blades, etc.) when UV lamps are installed. There was one > negative comment recently about " UV killing spores whizzing by. " I for one > believe it does work, although, like any engineering control, there are > limitations. If the air speed (velocity) is really high and the UV lamp > energy is low, there is a significant reduction in effect. If poorly > designed/installed, the benefits of UV irradiation can be negligible. The > lamps I have installed in HVAC systems are REALLY strong and warrant LOTO > controls so they are not energized when the HVAC system is worked on, or if > filters are changed. Moreover, they are shielded on the upstream side so > debris/particulates do not impact and soil the bulbs. I usually place the > lamps 4 to 6 inches from the heat exchanger (HE) on the upwind side, and > rarely am I installing less than three lamps. I don't like placing them in > dirty HVAC systems and when I install them on a retrofit, it is after the > system is thoroughly cleaned. In side by side comparisons, i.e., HEs with > lamps versus HEs without lamps, the cleanliness of the HEs with lamps could > be easily seen one year later. In fact, the HEs (with lamps) looked as > clean as the day the lamps were installed, while the other HEs had visible > dirt on them. There is a lot to designing and installing UV systems in HVAC > systems to make them effective - it is NOT a plug-n-play control. I know > Kaiser Permanente has invested heavily in UV irradiation of their HVAC > systems in an effort to control infection. I believe their results are > really supportive of UV irradiation. A big advantage of UV irradiation is > the low cost to operate. A big disadvantage is the high cost of each (good > quality) bulb, and several bulbs are needed in each fan unit on small > package units. On buildings with a centralized HVAC system (versus > individual roof-mounted package units) there could be 20 to 30 bulbs, or > more. Moreover, the HVAC fan unit must be so located that is can be easily > serviced (not a problem with centralized HVAC systems). This is not the > case in most residential construction because most architects/contractors > design and place the fan unit in the attic...a very convenient but really > dumb place to put a piece of machinery that needs periodic service with > filters that warrant frequent replacing. > > If I had a house that had central air (I don't, we open windows) I would > install UV irradiation along with an appropriate, well-sealed, HPFF filter > bank; and it would deliver the cleanest air at the best, and lowest, > operating cost. I am a believer in UV. > > For what it is worth... > -- > Geyer, PE, CIH, CSP > President > KENTEC Industries, Inc. > Bakersfield, California > www.kerntecindustries.com > > > > > > > >> Hi all, >> >> Not too long ago, AirwaysEnv@... wrote: >> >>> Unfortunately, science and scientists do not exist outside of >>> economics and finance. It can be seen in the way new technologies >>> are marketed today that the line between science and marketing gets >>> fuzzier and fuzzier. How about all these pharmaceutical >>> advertisements on television today? Or ozone generating air >>> purifiers. Or the science behind UV light bulbs in ducts to kill >>> mold spores whizzing by... >> >> I thought that the science behind germicidal UV was sound. Anyone have >> any thoughts on the matter? >> >> Thanks, >> Quote Link to comment Share on other sites More sharing options...
Guest guest Posted April 10, 2006 Report Share Posted April 10, 2006 There was one negative comment recently about "UV killing spores whizzing by." I for one believe it does work, although, like any engineering control, there are limitations. If the air speed (velocity) is really high and the UV lamp energy is low, there is a significant reduction in effect. If poorly designed/installed, the benefits of UV irradiation can be negligible. Question: Why doesn't UV from the sun kill mold spores floating around outdoors on a bright, sunny day? I've had some very high outdoor counts in sunny, summer weather. Steve Temes Quote Link to comment Share on other sites More sharing options...
Guest guest Posted April 10, 2006 Report Share Posted April 10, 2006 1. I took a quick look at outdoor today (very sunny) with a radiometer. Vis Light (>400 to 700 nm wavelength) >200 foot-candles UVB (315-385 nm) 40 uW/cm2 UVC (<285 nm) 40 uW/cm2 2. I do recall an article on diurnal (night/day) variations in mold viability with UV as cited causation. Other major factor dark (Demitiaceous) vs clear (hyaline). This last part or dark vs light can also be seen in differences between inside and outside mold species with regard to survivability and frequency of occurrence (dark better outside and clear inside). Tony ........................................................................... " Tony " Havics, CHMM, CIH, PE pH2, LLC PO Box 34140 Indianapolis, IN 46234 cell 90% of Risk Management is knowing where to place the decimal point...any consultant can give you the other 10%â„ This message is from pH2. This message and any attachments may contain legally privileged or confidential information, and are intended only for the individual or entity identified above as the addressee. If you are not the addressee, or if this message has been addressed to you in error, you are not authorized to read, copy, or distribute this message and any attachments, and we ask that you please delete this message and attachments (including all copies) and notify the sender by return e-mail or by phone at . Delivery of this message and any attachments to any person other than the intended recipient(s) is not intended in any way to waive confidentiality or a privilege. All personal messages express views only of the sender, which are not to be attributed to pH2 and may not be copied or distributed without this statement. Re: efficacy of germicidal UV Steve, It is the intensity of the UV that kills the bacteria and mold. I don't recall the exact numbers but UV biosafety hood lights are about 100 or more times more intense than sun light. Bob FAIR USE NOTICE: This site contains copyrighted material the use of which has not always been specifically authorized by the copyright owner. We are making such material available in our efforts to advance understanding of environmental, political, human rights, economic, democracy, scientific, and social justice issues, etc. We believe this constitutes a 'fair use' of any such copyrighted material as provided for in section 107 of the US Copyright Law. In accordance with Title 17 U.S.C. Section 107, the material on this site is distributed without profit to those who have expressed a prior interest in receiving the included information for research and educational purposes. For more information go to: http://www.law.cornell.edu/uscode/17/107.shtml. If you wish to use copyrighted material from this site for purposes of your own that go beyond 'fair use', you must obtain permission from the copyright owner. Quote Link to comment Share on other sites More sharing options...
Guest guest Posted April 10, 2006 Report Share Posted April 10, 2006 Mike, You are doing it right. It is extremely rare to find mold on a filter (compared to finding it on the coil or lining) so why bother to kill the biomass. It's much more important to keep the bulb clean. C. May May Indoor Air Investigations LLC 1522 Cambridge Street Cambridge, MA 02139 www.mayindoorair.com www.myhouseiskillingme.com Geyer writes: > Curtis: > > Most filter media will break down with as little as 20 to 40 hours of > direct, high-intensity UV irradiation. I always install UV lamps downstream > of the filter fabric this also helps keep the bulbs cleaner. Though I > have heard the arguments for placing UV bulbs upstream of the filter fabric > to kill the trapped boimass, I feel this is a mistake because few filter > fabrics will maintain filtration efficiency when exposed to the UV energy; > albeit, I imagine weak UV bulbs will have little effect on the fabric, they > will also have little effect on the biomass. > > -- > Geyer, PE, CIH, CSP > President > KENTEC Industries, Inc. > Bakersfield, California > www.kerntecindustries.com > Quote Link to comment Share on other sites More sharing options...
Guest guest Posted April 10, 2006 Report Share Posted April 10, 2006 Matt, Slight correction: D = I · t D = UV Dose, mW×s/cm2 I = Intensity, mW/cm2 t = Exposure time, s http://www.epa.gov/OGWDW/mdbp/word/alter/chapt_8.doc "Research indicates that when microorganisms are exposed to UV radiation, a constant fraction of the living population is inactivated during each progressive increment in time. This dose-response relationship for germicidal effect indicates that high intensity UV energy over a short period of time would provide the same kill as a lower intensity UV energy at a proportionally longer period of time." Outdoor spores should have long exposure time of several hours... Wei Tang QLAB Matt Klein wrote: It is the intensity of the UV that kills the bacteria and mold. I don't recall the exact numbers but UV biosafety hood lights are about 100 or more times more intense than sun light.Bob, I have to make a slight correction here. The dose is the poison. Intensity is just part of that equation. For UV, dose = intensity + exposure time with the correct wavelength for the biologicals of interest. For a kill, biologicals on surfaces can be exposed to lower intensity light because they can be exposed for a much longer time than those floating through the light in an air stream. The latter require much more intense light because exposure time is so short. Note that I know I am presenting the simplistic picture. Other factors, such as moisture and dust concentrations can impact exposure. ******************************************************If what is written looks too stupid to be written by me, I disclaim it. Onthe other hand, if it is brilliant, then I have no one to blame but myself. Otherwise, whether you choose to accept my opinion is up to you.****************************************************** K. Klein, PE ME, MBAIndoor Air Quality Solutions, Inc.2523 SR 133Bethel, OH 45106-0007VOICE: FAX: (with notice)E-mail: mkklein68@...*******************************************************Wouldn't it be nice if common sense were really common? Wei Tang, Ph.D.Lab DirectorQLABCherry Hill, NJ Quote Link to comment Share on other sites More sharing options...
Guest guest Posted April 10, 2006 Report Share Posted April 10, 2006 Matt, You are correct. It is the dose that is the critical item. However, with UV, most species, including humans have adjusted to a background level of radiation. Either the cells repair the damage or their DNA is immune. This level of UV (was?) in the normal range in the environment. Now with the loss of the ozone layer, UV radiation is at least 10-15% higher and much higher in some places. I know that there is some reported skin(sun) burn affected reported in southern argentina and chile. However, the effect on soil microbes and on arctic microbes has not been reported that I am aware of. So in order for UV to cause sufficient DNA damage to render mold spores or bacteria non viable, a minimum intensity is necessary. There is also the UV A verses UV B issue. On a humorous note, In the movies, one sees people being exposed to UV to sterilize their skin from outer space microbes. The amount of UV necessary to kill microbes from out space, would also kill the people.-post toasties. Bob Quote Link to comment Share on other sites More sharing options...
Guest guest Posted April 10, 2006 Report Share Posted April 10, 2006 "Outdoor spores should have long exposure time of several hours... "or several minutes if they were just released, or several days if they have been floating around, depending which spores in the air you are referring to. There should be a mixture of them unless it's right after rainfall, which washs away most of them. The sproes released after that should be more uniform. The UV lamp in HVAC would be providing additional dosage on top of the dosage from sunlight for spores from outdoors. D = (I(sun) x T(sun)) + (I(lamp) x T (lamp)) Wei Tang QLAB Wei Tang wrote: Matt, Slight correction: D = I · t D = UV Dose, mW×s/cm2 I = Intensity, mW/cm2 t = Exposure time, s http://www.epa.gov/OGWDW/mdbp/word/alter/chapt_8.doc "Research indicates that when microorganisms are exposed to UV radiation, a constant fraction of the living population is inactivated during each progressive increment in time. This dose-response relationship for germicidal effect indicates that high intensity UV energy over a short period of time would provide the same kill as a lower intensity UV energy at a proportionally longer period of time." Outdoor spores should have long exposure time of several hours... Wei Tang QLAB Matt Klein wrote: It is the intensity of the UV that kills the bacteria and mold. I don't recall the exact numbers but UV biosafety hood lights are about 100 or more times more intense than sun light.Bob, I have to make a slight correction here. The dose is the poison. Intensity is just part of that equation. For UV, dose = intensity + exposure time with the correct wavelength for the biologicals of interest. For a kill, biologicals on surfaces can be exposed to lower intensity light because they can be exposed for a much longer time than those floating through the light in an air stream. The latter require much more intense light because exposure time is so short. Note that I know I am presenting the simplistic picture. Other factors, such as moisture and dust concentrations can impact exposure. ******************************************************If what is written looks too stupid to be written by me, I disclaim it. Onthe other hand, if it is brilliant, then I have no one to blame but myself. Otherwise, whether you choose to accept my opinion is up to you.****************************************************** K. Klein, PE ME, MBAIndoor Air Quality Solutions, Inc.2523 SR 133Bethel, OH 45106-0007VOICE: FAX: (with notice)E-mail: mkklein68@...*******************************************************Wouldn't it be nice if common sense were really common? Wei Tang, Ph.D.Lab DirectorQLABCherry Hill, NJWei Tang, Ph.D.Lab DirectorQLABCherry Hill, NJ Quote Link to comment Share on other sites More sharing options...